7 GENS

02/15/2009 4:58 PM

7 GENS IN PARALELL KVAR IS HIGH ON TWO MACHINES WITH 2.5MW ON EACH MACHINE THE HIGH KVAR READING IS 1145 SHOULD WE INCREASE OR DECREASE DROOP TO SHARE KVARS MORE EFFICENTLY

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#1

Re: 7 GENS

02/15/2009 7:00 PM

The first thing you should do (apart from stop shouting) is to check WHY two of your parallel gen sets are not sharing the load. Unbalancing the generation system without understanding what is actually going on is likely to make the problem worse, not better.

__________________
jack of all trades
Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#2

Re: 7 GENS

02/15/2009 8:12 PM

What size are the generators? What is the load on each generator?

Register to Reply
Anonymous Poster
#3

Re: 7 GENS

02/15/2009 8:57 PM

Droop refers to KW load sharing. KVAR is related to the excitation, adjust the regulator setpoints (i.e. voltage) of the units not the droop. It almost sounds like you have 5 units in manual and two in auto voltage control?

Register to Reply
Anonymous Poster
#4

Re: 7 GENS

02/15/2009 9:56 PM

the gens are 2.5mw, once they are in paralell the voltage can not be changed individually. what can i do

Register to Reply Off Topic (Score 4)
Anonymous Poster
#5
In reply to #4

Re: 7 GENS

02/16/2009 11:31 AM

Once they are in parallel, adjusting what would have been the voltage before paralleling would adjust the KVAR.

Register to Reply