Pressure Testing a Transformer Tank

02/18/2009 5:13 AM

Can tank of corrugated win wall type of 1000kVA/22/0.4kV (IEC 60076) distribution transformer endures a pressure test of 0.5bar, duration:5h without any over - expanding or damage?

Corrugated fin wall: deepth:330mm, heighth:1100mm, total length:1200mm.

Are there standard test values of pressure for this kind of test of transformer tank?

Many thanks

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Engineering Fields - Control Engineering - New Member China - Member - New Member

Join Date: Sep 2006
Location: CHINA
Posts: 2945
Good Answers: 14
#1

Re: Pressure test of transfomer tank

02/18/2009 7:06 AM

0.5bar? negtive pressure?

joking? or are you going to write 0.5MPa?

Register to Reply
Commentator

Join Date: Oct 2007
Location: Caribbean
Posts: 79
Good Answers: 2
#2

Re: Pressure Testing a Transformer Tank

02/19/2009 8:30 AM

Transformers are pressure tested to ensure that they can withstand pressures in this range especially if they are inert gas blanketted , nitrogen in most cases .

Typical inert gas pressure can be 0.1 to 0.4 bars.

transformer s which are not inert gas blanketted normally operate at near atmospheric pressire because they will be invariably free-breathing , either to a conservator "bag" or to atmosphere. The free-breathing is required as the oil expand and contract with temperature.

Why , exactly, do you want to test the tank at 0.5 bars ( I assume gauge pressure ,, that is 0.5 bars above atmospheric which works out to be approx 7.5 psig) ?

Usually , the big question is whether the tank can withstand a vaccuum!!!!! And if it can , how much of a vaccuum.

__________________
Learn more, Do more , Be more
Register to Reply
Guru
Engineering Fields - Control Engineering - New Member China - Member - New Member

Join Date: Sep 2006
Location: CHINA
Posts: 2945
Good Answers: 14
#3
In reply to #2

Re: Pressure Testing a Transformer Tank

02/20/2009 1:46 AM

haha, you can laugh at me, i forget that oil should be at the vaccum station. sorry.

Register to Reply
Commentator

Join Date: Jun 2008
Posts: 80
Good Answers: 5
#4

Re: Pressure Testing a Transformer Tank

02/20/2009 12:10 PM

If you press it up quickly while it is energized you can do the extra "Lock-Out Test" also.

Register to Reply
Anonymous Poster
#5

Re: Pressure Testing a Transformer Tank

12/17/2009 11:38 PM

corrugated tank should be tested at 2.8 psi but it can withstand a pressure of 4.5 psi witout deformation.