Anonymous Poster

Earthing of facility equipments

11/06/2006 8:56 AM

pls, how do one calculate the sizes of the cables connecting the various equipments to the earth rods to enable adequate dissipation of power surge to the ground as necessary, without damage to the earthing system. Also, is there a standard earthing design? Other wise, how do one design one for a faciulity like 20 storey builiding having 3nos x 1000kva transformers, 5nos inductstrial generators etc?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Oct 2006
Location: Indonesia
Posts: 102
#1

Re: Earthing of facility equipments

11/06/2006 11:51 PM

Commonly, either the neutral or earthing conductor/cable size are sentenced to as minimum 1/2 of phase conductor/cable size, bigger than 1/2 of phase size is better, maximum is the same as phase conductor/cable size. Otherwise you are directed to calculate by the help of A = (Ix√t)/K.

Where, A : Earth conductor size (mm2), I : Fault Current (A), t : duration of fault or trip time of CB (seconds), and K : material coefficient.

What voltage ratio of your transformer? Primary and secondary? what the specification of generator? Commonly for 20kV/0.4kV at MVside use earthing mesh type by 70mmsq of BC copper. At LV side also use 70mmsq but by single rod. But you have to calculate.

Yes, definitely. there is a standard for earthing design DIN VDE, IEC, and IEEE, you have to contact to those related standard organization.

Regards,

Reply
Guru
Australia - Member - New Member Fans of Old Computers - H316 - New Member Hobbies - Model Rocketry - New Member

Join Date: Jun 2006
Location: Port Noarlunga, South Australia, AUSTRALIA (South of Adelaide)
Posts: 3048
Good Answers: 75
#2

Re: Earthing of facility equipments

11/07/2006 6:01 AM

This is nothing like the capacity that you are talking of but in my home I ran a separate power and earth circuit for all my electronic equipment. The earth consisted of a 12mmØ cable with short tails going to each of the outlets. The improvement in the quality of TV reception was quite remarkable and may people commented on how clear the picture was.

__________________
An elephant is a mouse built to government specifications.
Reply
Power-User

Join Date: May 2005
Posts: 244
Good Answers: 18
#4
In reply to #2

Re: Earthing of facility equipments

11/07/2006 12:31 PM

What masu is describing is the NEC standard technique called an "isolated ground" receptacle circuit. Hospitals are generally the only other place you'll find them. Used to be thought of as good for computer circuits, but it has been found to be orders-of-magnitude better to install all electronic circuits on a panel with line-noise suppression, and make sure the neutral is full size and not shared between circuits. Not as good as an isolation transformer, but close and cheaper.

*If you have a studio situation, go with a parallel 60+/60- system for zer0 noise.

Just make sure it is also bonded to the same grounding electrode system per the other standard NEC requirements.

__________________
Call it 'half empty' or 'half full' if you must, I've got the other half in a redundant glass...
Reply
Member

Join Date: Oct 2006
Location: Kennesaw, Georgia USA
Posts: 7
#3

Re: Earthing of facility equipments

11/07/2006 7:04 AM

The U.S. National Electrical Code (NEC) has a detailed calculation procedure and specific requirements for this type of grounding, and it expalins it much better than any of us could do on here.

Conversely, most any electrical design shop or electrical contractor with an engineering department can specify this for you pretty cheaply.

Reply
Power-User

Join Date: May 2005
Posts: 244
Good Answers: 18
#5

Re: Earthing of facility equipments

11/07/2006 12:34 PM

If you need an online resource, and don't have the current NEC or the IEEE handbooks available, I'd HIGHLY suggest you click on over to mikeholt.com, where you'll find detailed, graphic illustrations of what to do, online courses, and I think even some free video discussions. They also have an active forum for more detailed electrical-only questions, particularly if you are in the US and it's a Code issue.

__________________
Call it 'half empty' or 'half full' if you must, I've got the other half in a redundant glass...
Reply
Guru
Australia - Member - New Member Fans of Old Computers - H316 - New Member Hobbies - Model Rocketry - New Member

Join Date: Jun 2006
Location: Port Noarlunga, South Australia, AUSTRALIA (South of Adelaide)
Posts: 3048
Good Answers: 75
#6

Re: Earthing of facility equipments

11/07/2006 11:07 PM

PR1ME computers used the system too. PR1ME also used shielded power cables and line isolation transformers. The transformers were feroresonant and had the secondary effect of giving you a separate earth neutral link close to the computers. I managed to get a transformer and the cables from a computer room that was being decommissioned so it cost me nothing.

__________________
An elephant is a mouse built to government specifications.