Distribution Transformer - Maximum Safe Working Temperature

02/23/2009 5:17 AM

What is the maximum safe working temperature (for oil/Winding) of a distribution transformer of 500 KVA, 22000/433 Volts, which is loaded about 85%. It is used in outdoor environment.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Nov 2006
Location: OH USA
Posts: 549
Good Answers: 27
#1

Re: Distribution Transformer - Maximum Safe Working Temperature

02/23/2009 11:56 AM

If you are a user, the maximum safe working temperature is listed on the nameplate. That temperature will likely be shown as a rise temperature; meaning ______°C rise (over ambient). That will typically be 65°C over 40°C for conventional oil-filled transformers.

Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Dec 2008
Posts: 12
#2

Re: Distribution Transformer - Maximum Safe Working Temperature

02/23/2009 11:13 PM

NORMALLY TRANSFORMERS WILL BE CLASS A INSULATION.THAT IS 105 DEG C. HENCE GO FOR A WINDING TEMP OF MAX 90 DEG C, CONSIDERING THAT WTI has allways some error.

REG

E ANANDAN