Steam Turbines and Harmonic Distortion

03/02/2009 9:34 AM

Dear Sirs,

We have 11KV 8MW x3 sets steam turbine alternator in service on one of our FPSO. this plant is being commissioned and one of the observation in relation with the subject as follows and I need your view.

2 Turbine were running on load around 5 MW total (2.5+2.5) and we observed some vibration on the turbine side and also vibration level indicators went high and reached alarm level, it continued few hours. Every one running around the plant with the worries and trying all the stunt on steam side, condensate side, exhaust side to make sure there is no water carry over in the system, lubrication side also checked and all found normal, nothing could make out. finally it is found out that we have down hole heater connected to 11KV system load was increased to 50% from 25% causing load raise approximately by .8MW and the vibration also started at this time onwards. in order to conform we have brought down the heater back to 25% operation and vibration stopped. we feel harmonic distortion on power controller causing this turbine to vibrate!!!!!!!!!!! in order to do counter check load on TA increased similar load as heater by using some pumps, but turbine remain calm. if we start heater again, we are getting vibration. what could be the reason??, is it harmonics??? can harmonics disturbance on electrical system can reflect on prime mover???? or some grounding problem with the heater can cause this trouble??? Turbine alternator remain calm and no sign of any vibration etc..other than turbine vibration Please write your views.

thanks and best regards

K.Parimalam

Register to Reply
Pathfinder Tags: Harmonics and prime mover
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Associate

Join Date: Feb 2009
Location: Bluegrass Country of Kentucky
Posts: 29
Good Answers: 1
#1

Re: Harmonic distrotion reflecting on primemover

03/02/2009 10:30 AM

Definitely check the ground, a lot of times the problem with a system can be the ground. As for harmonics, if this is truly the problem, identify which harmonic order you have and then put a filter in to bleed that harmonic out to ground.

__________________
Joe the Electrical Contractor to the EOR, I know it was suppose to be in my base bid, but I still am going to submit a change order for it.
Register to Reply
Guru

Join Date: Mar 2007
Posts: 2550
Good Answers: 103
#2

Re: Harmonic distrotion reflecting on primemover

03/02/2009 11:17 AM

You are running 8MW turbines at 2.5MW ? is it not a bit of too low ?

a) There is a possibility of some vibrations on low load conditions. Did you check up with the supplier about this aspect

b) Do you have any sort of pf compensation ? Check that fellow's behaviour.

c) What is the type of Down hole heater? Indusction ? is it creating harmonics by interfering with the capacitance corresponding to the value of the 50% load ?

__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches
Register to Reply
Associate

Join Date: Feb 2009
Posts: 34
#3

Re: Steam Turbines and Harmonic Distortion

05/29/2009 2:23 AM

Dear All,

thanks for all your input. further test on this vibration reveled that we have a thyristor controller for process heater loading causing such vibration whenever temperature correction taking place. the controller is loading every 3 cycles once and causing this sort of vibration, presently we are running these controller on fixed output and managing situation.

Register to Reply
Register to Reply 3 comments
Copy to Clipboard

Users who posted comments:

Electron Plumber (1); parimalam (1); sb (1)