HT Power Factor Compensation

03/06/2009 5:42 AM

for our upcoming proj.We have to compensate for power factor at the HT side for 7 nos of 33 KV 1600KVA trafo.These trafo will be loaded by chillers for 12 hrs per day and remain on low loads for the reamining 12 hrs.can we have some soln without HT PF panels?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#1

Re: HT Power Factor Compensation

03/06/2009 11:51 AM

I am not sure what you are asking. Could you re-phrase the question?

Register to Reply
Anonymous Poster
#2

Re: HT Power Factor Compensation

03/07/2009 12:25 AM

7 transformers(1600KVA each) are connected to a 33 kv line.During no load we would like to improve the PF at the HT side (becos of trafo inductance).

Register to Reply
Guru

Join Date: Mar 2007
Posts: 2550
Good Answers: 103
#3

Re: HT Power Factor Compensation

03/07/2009 1:13 AM

The power factor contribytion of the transformers are supposed to be very low and considering you still have the core losses even on no load, I don't think any significant savinge will be achieved by putting the HT compensation.

However check the load pf and you will know whether you need the LT side compensation or not.

In fact since it is still under project stage, find out from your transformer supplier/ data supplied about the no load data and you will know. Typically the noload currents should be of the order of only 0.2% of FLA and at pf of say about 0.5 or so. Since the total current itself is so low, the effect on the total system average pf will not be significant even if the loads are off 50% time.

However i will put more significance to load compensations (ie LT side). It may typically come out much cheaper and the saving in power on HT may not prove more economical.

__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches
Register to Reply
Guru

Join Date: Jul 2008
Location: SoCal USA
Posts: 556
Good Answers: 23
#4

Re: HT Power Factor Compensation

03/07/2009 6:26 AM

A simple question: since power factor represents the timing of the amps compared to the voltage, and the only current at "no load" is through the resistance of the transformer coils only, what power factor are you talking about?

There is no lagging PF if there is only resistive loads.

In point of fact the only reason you can connect 33 kV across a thick length of copper wire without it melting is the fact that it is coiled, and so generates equal and opposite inductive voltage to buck the 33 kV, except for the minuscule current through the resistance alone which produces a small amount of heat and a faint hum.

Think about what removing that inductance would look like.

regards, CJM

__________________
I do not 'know it all', but i will admit that I would like to. CJM
Register to Reply
Guru

Join Date: Mar 2007
Posts: 2550
Good Answers: 103
#5
In reply to #4

Re: HT Power Factor Compensation

03/07/2009 7:38 AM

the only reason you can connect 33 kV across a thick length of copper wire without it melting is you are going to go up in smoke/ supply breaker at generator will trip .

PS: magnetising current of core.

__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches
Register to Reply Off Topic (Score 5)
Guru

Join Date: Jul 2008
Location: SoCal USA
Posts: 556
Good Answers: 23
#6
In reply to #5

Re: HT Power Factor Compensation

03/07/2009 3:15 PM

I learned it by the term CEMF, counter electro-motive force. My dad taught me as a young boy that coils generate when a current passes through, but in the opposite direction, and the technical term I learned, CEMF, made sense. It is the reason that transformers with no secondary load can be energized and they are at almost no primary current.

The current in the secondary coil winding will flow in the reverse direction compared to the primary current once a load is attached, since it is getting this Counter-emf induced into it also.

Since the CEMF acts as a braking force to the primary current, drawing secondary current reduces the braking force and the primary current begins to flow. The more CEMF that is drawn from the secondary coil into loads, the faster the primary current can flow. Drop a wrench across the secondary coil terminals, the brakes are gone, and the primary coil looks just like a large straight copper short across the primary and melts down.

My dad could draw some pretty great pictures with words. Later, when I learned the math and the technical details, I could better understand what was happening physically. So rather than just get to know the formula, I understood it.

Oh yes, by the way, I have learned a few good lessons from the "smoke test" method. They are not easily forgotten that way.

__________________
I do not 'know it all', but i will admit that I would like to. CJM
Register to Reply Off Topic (Score 5)
Guru

Join Date: Mar 2007
Posts: 2550
Good Answers: 103
#7
In reply to #6

Re: HT Power Factor Compensation

03/08/2009 3:58 AM

In fact when the secondary is OC, the easier way to visualise it is as an iron core inductor. The OC secondary is as good as non-existant.

Being Inductor, it has its L and hence lagging current and Iron Core, it has its iron losses and hence R (equivalent).

This creates a power factor at no load (which is non zero - power factor)

Due to the high inductance (and hence low I90o) and the primary iron losses(the I0o ) - which though low still becomes significant when the total I itself is low-the pf is quite away from zero.

__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches
Register to Reply Off Topic (Score 5)
Anonymous Poster
#8

Re: HT Power Factor Compensation

03/08/2009 11:56 PM

so if the no load losses are 5 KW for each trafo ,i would get some value of Pf capacitor which should compensate for the lagging pf.

Register to Reply
Guru

Join Date: Mar 2007
Posts: 2550
Good Answers: 103
#9
In reply to #8

Re: HT Power Factor Compensation

03/09/2009 2:15 AM

Please understand there is a huge difefrence between no load loss and pf.

Let us say at no load

Inl = Inl(0o) + Inl(90o)

The

Inl(0o) Corresponds to the losses in the transformers (cu losses, Eddy losses etc)

Inl(90o) Corresponds to the inductance of the transformers ( the current required to generate the magnetic flux)

Based on these two, you can gave a Capacitor which compensates by supplying

Inl(-90o) Thereby making

Inl = Inl(0o) + Inl(90o)+ Inl(-90o)= Inl(0o)

However when there is a secondary load

ILs = Ils(0o) + Ils(90o)

ILp = The total current in primary (corresponding to ILs )

= n (Ils(0o) + Ils(90o)) , n = transformer ratio

= Ilp(0o) + Ilp(90o)

Now the total primary current to be compensated is

Ip = Inl(0o) + Inl(90o) + Ilp(0o) + Ilp(90o) = (Inl(0o) + Ilp(0o)) + (Inl(90o) + Ilp(90o))

And the capacitor has to compensate by providing a current

Inl(-90o) + Ilp(-90o)

This current is going to be much more dependant upon load simply because

Inl(90o) << Ilp(90o)

Hence we go for compansating for load specifically and not much bother about comenasting the transformer per se.

The added advantage of compesating load (on secondary) is there when you have loads distributed - the line losses can be reduced for individual compensation at a poin nearer to load (this is already being discussed elsewhere)

__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches