transformer

03/14/2009 5:47 AM

how much load is given to tranformers

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Commentator

Join Date: Jan 2009
Posts: 62
Good Answers: 4
#1

Re: transformer

03/14/2009 6:09 AM

Transformer manufacturers recommend a maximum overload of 125% at rated temperature.

Heat is the number one enemy of transformers. If the ambient temperature for example is 42 deg Celsius, you can not load your transformer at its rated kVA.

If you can control the temperature buildup inside the transformer, practically, you can load a 100 kVA transformer with 500 kVA or more.

See IEEE standards for loading transformers at different temperatures.

__________________
Patriotism is the last refuge of scoundrels
Reply
Commentator

Join Date: Mar 2009
Location: delhi india
Posts: 79
Good Answers: 2
#2

Re: transformer

03/14/2009 6:51 AM

you can take 80% efficiancy of atransformer at safe level

Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#3
In reply to #2

Re: transformer

03/14/2009 6:10 PM

The amount of load depends on overall power factor (p.f) of the load.

The load in KW (or MW) = Transformer KVA (MVA) x overall p.f (cosØ) of the load.

The power factor depends on the type of loads; the p.f for the induction motors is close to 0.8.

Thanks,

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)