Heavy Rain and 500-KV HT Tower Line

03/24/2009 12:30 AM

Dear All electrical Gurus,

I have a doubt why during heavy down pour and rain water is dipped over the high voltage 500Kv tower line of country wide grid system didnt 'flash-over' or short circuit in between L to L ? (Sorry if i have ask stupid Q )

I noticed when there is an insulation breakdown at the HT 22Kv or lower on the cable termination kits can caused flash over and blow the whole cable kit and even switch gear ?

Thank you and very best regards

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Member

Join Date: Mar 2009
Posts: 9
#1

Re: Heavy rain over the 500kv HT tower line

03/24/2009 1:27 AM

for short circuiting there are certain conditions which are to be fullfild first first as you know the basic requirement for short circut of current flow it need a continious path or potential difference regarding potential difference as b/w tow line there is phase difference which can cause flow of current but as for continious path is concern raining do not provide a continious path b/w two lines..

Register to Reply
Commentator

Join Date: Mar 2009
Location: delhi india
Posts: 79
Good Answers: 2
#2
In reply to #1

Re: Heavy rain over the 500kv HT tower line

03/24/2009 3:58 AM

during rain water drop fall only on one line so no contect take place between two line .it is same as a bird sitting on one line did not get any shock due to uncompletion of ckt

Register to Reply Score 1 for Good Answer
2
Guru

Join Date: Nov 2006
Location: OH USA
Posts: 549
Good Answers: 27
#3

Re: Heavy rain over the 500kv HT tower line

03/24/2009 10:40 AM

That's the primary reason insulators have weathersheds. Those weathersheds break up the water drip path and provide protected creep to withstand system voltage under wet and contaminated conditions. The primary insulation is air so insulators and insulated housings are designed such that they will not reduce the dielectric strength of air under any condition, with the exception of direct lightning strokes.

Register to Reply Good Answer (Score 2)
Power-User

Join Date: Mar 2009
Posts: 130
#6
In reply to #3

Re: Heavy rain over the 500kv HT tower line

03/24/2009 8:20 PM

Dear Bluestone

Thank you very much of your good answer

Regards

Register to Reply
3
Guru

Join Date: Mar 2007
Posts: 2550
Good Answers: 103
#4

Re: Heavy rain over the 500kv HT tower line

03/24/2009 1:49 PM

The insulators are of an umbrella shaped. There is a metallic cap on the top of each disc, which is fastened to the top disc. This metal helps in equalizing the voltage drops across insulators.

Due to umbrella shape along with the circular ripples on bottom,

a) the top water (rain) sprays away

b) the water is unable to creep through these ribs to the metal cap/ conductor

c) The arc creep (sometimes the arc passes through the surface of the insulator as the better pathway than arcing through air) gets a longer path.

d) Additionaly these ceramics are glazed and has a high finish (not matty) to reduce the creep further.

e) The line to line arcing due to high diatance between lines is highly unlikely with air breakdown voltage about 30KV/inch or so.

f) The more probable line-earth fault is avoided as above. A rough sketch is enclosed explaining (made almost free hand and not to scale )

__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches
Register to Reply Good Answer (Score 3)
Power-User

Join Date: Mar 2009
Posts: 130
#5
In reply to #4

Re: Heavy rain over the 500kv HT tower line

03/24/2009 8:18 PM

Dear sb Guru,

Thank you very much for your very good answer.

Regards

Register to Reply
Guru

Join Date: Dec 2005
Posts: 1602
Good Answers: 19
#7
In reply to #4

Re: Heavy rain over the 500kv HT tower line

03/24/2009 11:00 PM

Good answer Mr. Bluestone and excellent picture Mr. sb.

To add to bluestone's comment on environmental contamination, the insulators must be periodically maintained to remove the dirt film that does build up over time. If too much film builds up, the water does not shed properly and can cause a short when the insulator gets dirty and wet enough. I learned this during a plant electrical shutdown when the utility was replacing the main service transformer. They were amazed at how dirty the 34.5KV insulators were from cooling tower overspray, and surprised we had not previously shorted out during rain. In this case, we were lucky, but it does occasionally happen.

__________________
Eventually, one needs to realize that it is far less important to be the smartest person in the room than it is to sit next to that person and make friends.
Register to Reply
Anonymous Poster
#11
In reply to #7

Re: Heavy rain over the 500kv HT tower line

03/25/2009 7:53 AM

Cleaning of insulators was an annual requirement at an industry where I used to work.We maintained all equipment from 13.2KV. down to 120 vac outlets in the plant.Switchgear,insulators,bus bars,transfomers,etc. all require periodic maintenence to ensure reliability.I have seen the results of CATASTROPHIC arcing, where 1/2 inch thick steel girders were turned into molten puddles.According to witnesses, it looked and sounded like a bomb.

Register to Reply
Anonymous Poster
#14
In reply to #11

Re: Heavy rain over the 500kv HT tower line

04/21/2010 3:01 AM

Dear , We produce the steel towers , like as telecom steel tower ,guyed mast , electric power line , and we can supply the design of them . So if there is any question , please send it to qdhistro@yahoo.com.cn , Here is our website :www.histro.com.cn    www.histro.net.cn

Register to Reply Off Topic (Score 5)
Anonymous Poster
#12
In reply to #4

Re: Heavy rain over the 500kv HT tower line

03/25/2009 10:35 AM

Most excellent answer dude.

Register to Reply Off Topic (Score 5)
Guru
Popular Science - Cosmology - Let's keep knowledge expanding Engineering Fields - Retired Engineers / Mentors - Hobbies - HAM Radio - New Member

Join Date: Dec 2006
Location: North America, Earth
Posts: 4528
Good Answers: 106
#8

Re: Heavy Rain and 500-KV HT Tower Line

03/24/2009 11:28 PM

Hi aikhh,

Pure water is not a conductor of electricity. It takes some contamination such as salt to make it conductive. If there is enough air pollution, it may pick up enough to have some measurable conductivity. There is no such thing as a stupid question, but you may get some stupid answers. Hope this is not considered one!

S

__________________
“I would rather have questions that can't be answered than answers that can't be questioned.” - Richard Feynman
Register to Reply
Power-User

Join Date: Mar 2009
Posts: 130
#9
In reply to #8

Re: Heavy Rain and 500-KV HT Tower Line

03/25/2009 12:40 AM

Thank you very much StandardsGuy , I like your sentence :

"There is no such thing as a stupid question "

Regards

Register to Reply
Guru

Join Date: Nov 2006
Location: OH USA
Posts: 549
Good Answers: 27
#13
In reply to #8

Re: Heavy Rain and 500-KV HT Tower Line

03/25/2009 11:36 AM

Contamination flashover of insulators is interesting and I've spent a good share of my life designing, developing, testing and applying insulators of all types. Your comment about pure water is correct; but more correctly, deionized water is non-conductive. In fact, deionized water can be used as an insulator. (I've used it with inline deionizers in closed cycle cooling loops between energized thyrister valves and refrigeration units on the ground). Clean atmospheric rain water is ionic but not usually highly conductive.

Contamination flashover will not generally occur during heavy rain. Heavy rain tends to wash and remove water-soluble contaminants from exposed insulation surfaces.

Power frequency contamination flashover generally occurs when contaminated insulator surfaces are lightly wetted by mist, light rain, heavy fog, wet snow, etc. Water soluble contaminants become conductive and leakage currents begin to flow over the insulator surface. Those currents do not flow through the contamination layer but rather along the interface between the insulator surface and the contamination. The worst type of contaminant is hard, crusty contamination such as dust from nearby cement plants, gypsum, fertilizer, and similar materials because it usually cannot be removed by natural rainfall washing. Removal requires high pressure water washing or removal by abrasive blasting with walnut shells or other media.

Anyway, the leakage currents can generate very high temperatures in the interface that may craze the glaze on porcelain insulators, etch glass insulators and track some types of polymer or non-ceramic insulators. The evidence is usually dendritic or tree like patterns on those surfaces. A similar condition can occur on ice-covered insulators. Usually not a problem until the ice begins to melt and leakage currents begin to flow in the liquid interface between the insulator and the ice.

One cardinal rule with insulators and that is they only fail in interfaces.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#10

Re: Heavy Rain and 500-KV HT Tower Line

03/25/2009 3:26 AM

The clearence is suitably designed on tower lines between conductors taking the possibility of the swing of conductors under certain conditions like wind etc so that phase to phase short is not likely.As regards insulators the clearence is very high and in towers nearing the substation u will see horn gaps in addition which ensures the flash over is in the gap and it does not travel to the substation.In addition hot line washing of insulators is adopted which ensures contamination and hence breakdown doe not take place.The only thing on a rainy day is coronna losses increase

__________________
To avoid crticism do nothing,say nothing,be nothing
Register to Reply Score 1 for Good Answer
Register to Reply 14 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: