Temperature Rise for Class F Insulation

03/24/2009 7:44 AM

Dear all

i'd like to know What is the temp rise limit for class f insulation (induction motor)?

Does this value change with ambient temperature?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
3
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#1

Re: temp rise, class f insulation

03/24/2009 8:47 AM

Please see the below Chart and you will get your answer:

Ins. Class

Max Temp.

Amb. Temp.

Temp. Rise

Hot Spot Allow.

A105°C40°C55°C10°C
B130°C40°C80°C10°C
F155°C40°C105°C10°C
H180°C40°C130°C10°C

Note: Hot Spot Allowance - The value that takes into account the additional temperature variations within the inaccessible spots of a motor winding. These spots are located in the stator slots or coil heads. 10° C is considered a standard for design purposes.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply Good Answer (Score 3)
Guru
Safety - ESD - New Member Popular Science - Cosmology - Amateur Astronomer Technical Fields - Technical Writing - Writer India - Member - Regular CR4 participant Engineering Fields - Optical Engineering - New Member

Join Date: Dec 2007
Location: 18 29 N 73 57E
Posts: 1390
Good Answers: 31
#2
In reply to #1

Re: temp rise, class f insulation

03/24/2009 11:01 PM

Just some addition:

Ins Class E: Max Temp 180°C,

Temperature Rise (Max temp - Amb Temp). Here temp rise is inclusive of hot spot allowance.

Thus if amb temp is 25°C, permitted temp rise (total) will be (180-25)= 155°C.

Register to Reply
Power-User

Join Date: Sep 2007
Location: Sheboygan, WI USA
Posts: 372
Good Answers: 13
#3

Re: Temperature Rise for Class F Insulation

03/24/2009 11:04 PM

As I recall, The stator slot RTD temperature shutdown was set at 250F on the hydro generators with class F insulation.

__________________
"I believe we are masters of our lives - we hold all the cards and it is up to us to use them right." Vesna Vulova - survived 33,000ft fall
Register to Reply
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#4

Re: Temperature Rise for Class F Insulation

03/24/2009 11:55 PM

Max temp. rise permisible inclusive of ambient by resitance method is 140 DegC earlier .The max temp allowed is 155 Deg with 10 Deg for hot spot .If ambient is 40 rise by resistance method to be limited to100 deg C.By thermometer method it is to be limited to 95Deg C.If ambient temp is 50 then temp rise will be 90 deg. Ambient depends upon motor manufacturer's design.Normally availble standard motors are designed for 40Deg .Motors are designed specifically for 45 and 50 deg against requirements.

__________________
To avoid crticism do nothing,say nothing,be nothing
Register to Reply
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#5

Re: Temperature Rise for Class F Insulation

03/25/2009 3:19 AM

Further to my post ,I would state that max temp including ambient is 145 DEg C now .therefore the max.temp rise over ambient of let's say 40 Deg will be 105 by resistance method of measurement and 95 for thermometer.It is the temp rise that the designer has allowed facilitates one to use the motor on higher ambient without reducing the out put.For example if a motor is having a temp rise of 90 DEG over 40Deg amb then with class F and class F rise one can use it up to 55DEG amb or at 40 It can be overloaded.However in India the temp rise is restricted to that of class B which means a total of 120DEG C Including ambient that is 80Deg rise over 40DEG by resistance .So while specifying one has to be clear about the requirement.

__________________
To avoid crticism do nothing,say nothing,be nothing
Register to Reply Score 1 for Good Answer
Register to Reply 5 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!