HV Switchgear Insulation Resistance

03/28/2009 3:19 AM

Hi,

Can anyone help me in showing where do can I get the standard of Minimum Insulation resistance for HV Switchgear. When I work at the factory I used to use " Voltage rating of the measured equipment / 1000 + 1 MOhm" as the minimum insulation resistance of the equipment; now I work at HV Substation ( 70 kV and 150 kV SS ), I don't know what is the right standard of this matter. For 70 kV CT I got 40,000 MOhm, 15 MVA Power transformer Phase to ground at 150 kV bushing even higher than that, it's about 200,000 MOhm with 10.000 Volt Insulation resistance tester.Recently I measured ABB 70 kV Potential transformer, I got at two units from phase R and S about 60,000 MOhm, and phase T only 12,000 MOhm I measured with 10,000 Volt Megger. Insulator has been cleaned properly,because I didn't know what is the minimum resistance allowed to energised this PT, base on my past experience I just put them into sevice. The result is OK untill today. Can anyone help me regarding this matter ? Thank you.

Stanyadji

Register to Reply
Pathfinder Tags: Insulation Resistance
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Active Contributor

Join Date: Dec 2008
Posts: 12
#1

Re: HV Switchgear Insulation Resistance

03/28/2009 3:27 AM

is that 1 minute value or ten minutes value.

reg

Register to Reply
Active Contributor

Join Date: Mar 2009
Location: Makassar, Central Indonesia
Posts: 15
#4
In reply to #1

Re: HV Switchgear Insulation Resistance

03/28/2009 8:53 AM

We did the IR test with Megger.

The one minute or ten minutes test is done with separate AC supply and we didn't do it.

Register to Reply
Anonymous Poster
#2

Re: HV Switchgear Insulation Resistance

03/28/2009 6:13 AM

You should ask the manufacturer for the minimum value allowable and one think is that I have observed that with the increase in voltage at which you are taking IR the value of IR decreases a little.Also you should measure Polarization index and then compare the values..

Register to Reply
Commentator

Join Date: Jan 2009
Posts: 62
Good Answers: 4
#3

Re: HV Switchgear Insulation Resistance

03/28/2009 7:23 AM

According to InterNational Electrical Testing Association reference book your voltage ratings require 100 MegOhms. This figure in my opinion is too conservative.

But based on my experience, this value is too high. We have energized and continued operating 69 kV power trnsformers and SF6 power ckt bkrs whose one minute insulation test readings fall between 10 - 50 MegOhms at ambient tempratures between 30 - 38 deg Celsius and humidity between 60 - 80%. And yes, we do clean the bushings before testing. We've been doing this for many years now and not one of our equipment failed.

We rely more on the Polarization Index and Tan Delta - sweep frequency/sweep voltage, although these take a lot of time to completely perform. Based on our experience, you can never go wrong on this two methods of insulation tests.

We've also tried the formula Ins. Res. = CE/(kVA)^0.5 and the 1 MegOhm per kV plus 1, but they all don't work for us.

Honestly, for me, interpreting IR test results is a lot more challenging compared to the tan delta.

__________________
Patriotism is the last refuge of scoundrels
Register to Reply
Active Contributor

Join Date: Mar 2009
Location: Makassar, Central Indonesia
Posts: 15
#5
In reply to #3

Re: HV Switchgear Insulation Resistance

03/28/2009 9:02 AM

We did the tan delta test for power transformer only.

We never apply it to CB, CT and CVT. Can you introduce the standard which required tan delta test for CB, CT and CVT; I would like to suggest it to PLN. ( Indonesia Electric Power Co. )

For your information our ambient temperature range is 29 - 32 degreeC and the humidity between 89 - 95%.

In my opinion its rather risky, to energise the switchgear who'r IR is only 10 MOhm, but this a good information,as long as the switchgear can operates safe and sound.

Register to Reply
Commentator

Join Date: Jan 2009
Posts: 62
Good Answers: 4
#6
In reply to #5

Re: HV Switchgear Insulation Resistance

03/29/2009 6:33 PM

Sorry for my typographical error in #3. It's "10 - 50 MegOhms GigaOhms."

Tan delta test can be performed on any type of equipment insulation. If you have the testing guide of Doble Engineering, it details and explains a lot. The tan delta test manual of Megger Intl is also a very good guide.

__________________
Patriotism is the last refuge of scoundrels
Register to Reply
Active Contributor

Join Date: Mar 2009
Location: Makassar, Central Indonesia
Posts: 15
#7
In reply to #6

Re: HV Switchgear Insulation Resistance

03/29/2009 8:14 PM

Thank you,

I'll contact my friend who is the agent of Doble at Indonesia regarding this matter.

regards,

Stanyadji