Batteries for 6.6kV Switchgear Panel

03/28/2009 11:03 AM

Hi Y'all,

I am planning the 110V DC power supply for a 6.6kV Motor Control Centre. The application requires the battery & charger to be placed in the plant along with the machinery and close to man movement.

Is it O.K. to use SMF (sealed, maintenance free) batteries in this case ?

I am trying to avoid using Vented Lead Acid batteries due to gas formation and maintenance issues.

Anybody tried it ?

__________________
We Are In Current Control !
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User

Join Date: Aug 2007
Location: Heilonjang China. 2 blocks from you
Posts: 109
Good Answers: 5
#1

Re: Batteries for 6.6kV Switchgear Panel

03/28/2009 6:54 PM

Sunilji,

You can go and have a look at barterries used in your substation, i don't think they use SMF for a reason i may think is that if any of the sets of the battery fails you will not know and charger will continue charging these batteries, if you have a system disturbance your system will fail since it was being powered by the charger.

About the gasses you may need to put an extration fun if its in an enclosed room.

__________________
poy
Register to Reply
Power-User

Join Date: Aug 2006
Posts: 183
Good Answers: 2
#2

Re: Batteries for 6.6kV Switchgear Panel

03/29/2009 12:03 AM

Dear Sunilji

While I agree to what Waco has already pointed out, but then you will have to decide, since location of the battery & charger is such that there will be human movement. SMF is not the best choice for substation application, one of the reasons has already been written by Waco. Other problem is due to temp. If the ambient is in excess of 35 deg. C then the electrolyte recombination in SMF battery reduces and after some time, it goes below the required level. Battery capacity also goes down and eventually fails, without giving any warning or indication.

Tubular lead acid battery requires separate room with ventilation and acid proof/resistant tiles for floor & requires maintenance but lasts much longer. I have even come across an instance wherein a company "forcibly" replaced the tubular lead acid battery after 19 years of installation, though it was still functioning. This is a rare case and most of the batteries will not last more than 8-10 years depending on maintenance etc. We supplied the charger for their new requirement.

We are an ISO 9001-2000 certified manufacturer of chargers with DB and supply complete system with battery ( SMF/tubular/NiCd, depending on customers requirement ) for power plants and substations. Apart from India we have installation in 12 other countries. Kindly send enquiry to uni_insta@dataone.in with cc to ashoktoshniwal@yahoo.com.

Thanks and regards

Ashok Toshniwal, Director - Universal Instruments Manufacturing Co. Pvt. Ltd., Bangalore, India

Register to Reply Score 1 for Good Answer
Anonymous Poster
#3

Re: Batteries for 6.6kV Switchgear Panel

03/29/2009 7:50 AM

www.enersys.com look at powersafe SBS-190 or anything in the Odyssey line up

need to have a three stage charger that has a minimum 13.6V in float

Register to Reply
Guru

Join Date: Jul 2008
Location: Mallorca, Spain
Posts: 567
Good Answers: 15
#4
In reply to #3

Re: Batteries for 6.6kV Switchgear Panel

03/29/2009 11:20 AM

"www.enersys.com look at powersafe SBS-190 or anything in the Odyssey line up

need to have a three stage charger that has a minimum 13.6V in float"

Isn't 13.6V alittle low for the float setting on a 110V bank?

Chas

__________________
En la casa del herrero, cuchillos de palo!
Register to Reply
Register to Reply 4 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); ashoktoshniwal (1); capblanc (1); olivinak (1)

Previous in Forum: Horsepower to watt   Next in Forum: one jumper of a line of 220 kv breaker opens

Advertisement