i want to know range of under voltage and over voltage to put the settings for the protection relay my source voltage is 400 volt and freq. 50HZ.and i want to know this from IEC standard .thx
Re: range of undervoltage and overvoltage
03/29/2009 2:47 PM
What is the application? Is this a motor protection relay? Have you consulted the manufacturer's website and/or performed a search of the internet for your answer?
03/30/2009 7:26 AM
variation should be between + or - 12% of 400V
03/30/2009 8:39 AM
Power company generally indicates what would be their %voltage flactuations (plus/Minus) of their system supply voltage. Now if your load side equipment require not to go below or above certain voltage (say no more than 415V for example for a costly equipment) to work with their 100% efficiency, then your over voltage should be set not more than 15x100/400=3.75%. Same way you may decide under voltage set point.