open delta

04/10/2009 10:02 PM

why we use open delta winding in RVT/PT for neutral displacement protection?

Register to Reply
Pathfinder Tags: A
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Active Contributor

Join Date: May 2008
Location: Bangalore,India
Posts: 10
#1

Re: open delta

04/11/2009 1:13 AM

Dear Friend

In midium voltage networks ( 33KV,66KV etc), Neutal displacement protection is provided. Neutral displacement protection relay is actuated by voltage of Open delta ( Primary is star and Secondary is open delta) winding of 3-ph, P.T.

So i suggest you go through protection hand book of GE Power/ABB or any good text book on Generator protection.

Bhushan

Register to Reply
Power-User

Join Date: Dec 2007
Location: Brasov, Romania
Posts: 255
Good Answers: 7
#2

Re: open delta

04/12/2009 7:17 AM

Open delta winding is able to detect the homopolar component in a three phase network. This component in voltage is given by ground faults. A medium voltage network is able to operate with a grounded phase for a while; the other two phases shall suffer overvoltage. If a generator is conected on a medium voltage busbar, an overvoltage may be dangerous for the ground insulation and this is a way to find out if occurs.

__________________
The time is ......now
Register to Reply
Power-User

Join Date: Oct 2008
Location: Jakarta Indonesia
Posts: 123
Good Answers: 7
#3

Re: open delta

04/15/2009 9:38 PM

Dear all,

I think the PT connection here should be called broken delta, since open delta is defined as:

"A connection similar to a delta-delta connection utilizing three single-phase transformers, but with one singe-phase transformer removed.... " in IEEE 100.

Regards

__________________
Akihito Shigeno @ JGC-Indonesia
Register to Reply
Anonymous Poster
#4

Re: open delta

10/21/2010 4:24 AM

open delta means two side of winding is opened and resultant voltage across open terminal is approximately zero due resultant vector sum of voltage

Register to Reply