What is galvanic isolation in terms of transformer ?
why it is used ?
Re: Galvanic isolation
04/18/2009 3:26 AM
DO YOU MEAN A SHIELD IN BETWEEN the primary & secondary winding ? it is normally used in controls & automation applications. This eliminates the 3rd & 5th harmonics to enter in to secondary winding thru line disturbances.
Normally, transformers used for plc controls / computer systems / vfd drives etc.... , evn control transformers are used in power supplies for isolation. Isolation means stopping the line disturbances / noise / electromagnetic noise /5th harmonics to enter in to the elctronic cards. There by improving the reliability in performance of the systems used.
Exploring the Science of Electricity
04/19/2009 12:09 PM
HI Guest
Galvanic isolation is the principle of isolating functional sections of electric systems so that charge-carrying particles cannot move from one section to another.
The galvanic isolation in a UPS is a complete physical separation between input and output and is achieved by means of transformers with physically different primary and secondary windings. These are often shielded from each other by an additional electrostatic plate to further reduce common mode-noise. With a fully galvanic isolation the output of the UPS can be considered as a derived source that can be grounded, or left floating depending on the application
Advantages:
1. Higher immunity against distortions in input mains;transient voltage surge will be reduced and thus secure a cleaner DC-Bus, which minimizes the risk of a malfunction of the Inverter connected to the DC-Bus.
2. Possibility to monitor and react on earth fault in the DCBus and battery bank ( No trip of the battery bank by earth fault, fault can be monitored and it's possible to react before system will shut down).
3. Reduction of harmonic current feed back to input mains.
4. No DC feedback by major failure in the Rectifier.
5. Higher safety while working on batteries for maintenance personnel.
-S
Good Answers: 15
04/19/2009 8:12 PM
In nautical use they are used to isolate the on board distribution from the shore supply in order to avoid earth fault currents causing galvanic corrosion.
Chas
04/20/2009 1:57 PM
Simply, galvainic isolation is the physical separation of electrical signals, as previously stated.
Often used as a physical barrier between two "ground" potentials. Often there is a voltage differential between grounding points. Sometimes it is small and insignificant. Sometimes it is large enough to cause problems.
04/20/2009 4:37 PM
All transformers have the windings galvanic isolated (not physically/hard connected with each other), energy flow occurs via electromagnetic coupling between them.
The only transformer type that does not have galvanically isolated windings is an autotransformer, which has the 2 windings interconnected so that one part of the total winding is part of both the primary and secondary winding.