Anonymous Poster

Air Conditioner Fuse VS Breaker Sizes

04/20/2009 9:26 AM

If air conditioner label says MOCP 30a... should both the fuse at the disconnect as well as the breaker at the panel be 30amps maximum?

I've had some people tell me to use 30a fuse at disconnect, but use larger breaker at the panel? Does the NEC permit using a larger breaker at the panel?

Brad

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Engineering Fields - Systems Engineering - New Member Popular Science - Weaponology - New Member

Join Date: Jun 2006
Location: Borrego Springs
Posts: 2636
Good Answers: 62
#1

Re: Air Conditioner fuse VS breaker sizes

04/20/2009 9:29 AM

The purpose of the breaker / fuse at the panel is to protect the wiring - so determine the capacity of the wiring with the distance to the load (roughly).

Unless you feed more than one circuit with that breaker. But large appliances are usually segregated for exactly this reason.

__________________
"If you want to get somewhere else, you must run at least twice as fast as that!"
Reply
Anonymous Poster
#2
In reply to #1

Re: Air Conditioner fuse VS breaker sizes

04/20/2009 9:45 AM

Ok, thanks.

So the wire size between the disconnect and the a/c compressor can/might be smaller than the feeder wire from disconnect back to the panel?

Reply
Guru
Engineering Fields - Systems Engineering - New Member Popular Science - Weaponology - New Member

Join Date: Jun 2006
Location: Borrego Springs
Posts: 2636
Good Answers: 62
#3

Re: Air Conditioner fuse VS breaker sizes

04/20/2009 9:58 AM

Unless the circuit is segregated - then a "mains" circuit would feed smaller circuits, like your disconnect.

Where is your electrician?

__________________
"If you want to get somewhere else, you must run at least twice as fast as that!"
Reply
Anonymous Poster
#4
In reply to #3

Re: Air Conditioner fuse VS breaker sizes

04/20/2009 10:30 AM

Just learning is all, not doing any wiring myself !

Just trying to understand whether or not a guy who puts a 30a fuse in a disconnect might need to use a 40a breaker at the panel. I can see by your answer why he would.

Thanks much

Brad

Reply
Anonymous Poster
#5

Re: Air Conditioner Fuse VS Breaker Sizes

04/21/2009 5:58 AM

I'd like to add that what you also should consider is the Minimum Circuit Ampacity (MCA). This spec. allows you to run the smallest gauge wire permitted, as long as you don't violate code.

Reply
Participant

Join Date: Apr 2009
Location: Norman, Oklahoma, USA
Posts: 1
#6

Re: Air Conditioner Fuse VS Breaker Sizes

04/21/2009 9:30 AM

You should, by all means, use the same breaker size as well as fuse size in the disconnect. This circuit is only for the a/c condenser only and nothing else should be aloud to operate on this circuit.

Reply
Anonymous Poster
#7

Re: Air Conditioner Fuse VS Breaker Sizes

04/23/2009 4:46 PM

guest;use a hvac rated breaker & a no fuse disconnect, why mess around with fuses?perry