Anonymous Poster

Earthing

04/22/2009 9:48 AM

I have a Panel having 40A,25kA incomer, please give me the earth cable size calculation

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Apr 2007
Posts: 577
Good Answers: 10
#1

Re: Earthing

04/22/2009 8:08 PM

From the cable data's you will require 4Cx16sq-mm size cable for your power and earthing or you can use 3Cx16sq-mm for your power and for earthing cable you can selects 10sq-mm or 16sq-mm

__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....
Reply
Associate

Join Date: Apr 2009
Location: Bangalore, INDIA
Posts: 34
#2

Re: Earthing

04/25/2009 3:34 AM

Use 4core(for RYBN) ,6 Sq.mm, Copper multi strand Flexible Cable.

& Earthing 10 sq mm copper.

In some cases, 5core cable of the same size is allowable.

__________________
"Strength does not come from physical capacity. It comes from indomitable will." Mahatma Gandhi
Reply
Anonymous Poster
#3

Re: Earthing

04/28/2009 5:42 AM

just asking...ur panel incoming is 40A but why your bus bar rating is 25KA...seem too high...or am i wrong...if you follow incoming cable, you can size ur earting either 16mm2 or a little bit lower..but if you size according to the fault level 25kA your earthing probably around 70mm2...refer to ieee std 80-2000 for additional info.