Maximun Neutral and Earthing Cable Size

04/22/2009 8:37 PM

Dear All Gurus,

I have a doubt in my mind for long time, i need electrical gurus explain a little more on this question to me please , If this electrical installation at power transformer / generator - main switch board system and final motor and power lighting circuitry - sub board system.

Why the up to dia 70mm² live conductor,the earth cable must be same size ?

Above dia 70mm² live conductor the earth conductor need to be only dia 70mm² ?

Thank you very much

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Participant

Join Date: Feb 2006
Posts: 4
#1

Re: Maximun Neutral and Earthing Cable Size

04/24/2009 5:20 AM

It depends on what protection you need ? Earth Fault Relay or Lightning equal potential.

If there is a leakage to earth ,the conductor must be the same,what goes in must come out at equal value , there is reason for you to have bigger conductor to reduce voltage and harmonic feedback.

Register to Reply
Anonymous Poster
#2

Re: Maximun Neutral and Earthing Cable Size

04/26/2009 7:15 PM

yes thesame size all

Register to Reply
2
Power-User
Ireland - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: Aug 2007
Location: Northern Ireland
Posts: 197
Good Answers: 17
#3

Re: Maximum Neutral and Earthing Cable Size

04/27/2009 6:30 AM

Unfortunately not very helpful or even relevant answers.

You ask a good question and deserve a proper answer.

The current carrying capacity of a cable refers to it carrying a continuous load. An earth cable normally carries no load, and under fault conditions will carry a significant instantaneous current but only for a short time - most Regulations define 0.1 to 5 sec - before the fuse or breaker trips. Its size therefore is defined by different calculating parameters.

Broadly speaking however the magnitude of earth fault current depends on:

(a) the external earth loop impedance of the installation (i.e. beyond the supply terminals)

(b) the impedance of the active conductor in fault

(c) the impedance of the earth cable.

i.e. Fault current = voltage / a + b + c

Now when the active conductor (b) is small, its impedance is much more than (a), so the earth (c) cable is sized to match. As the active conductor gets bigger, its impedance drops significantly below that of the external earth loop impedance (a); when quite large (here in NZ above 120mm2, but in your region apparently 70mm2) its impedance can be ignored. At this point there is no merit in increasing the earth cable size

i.e. Fault current = voltage / a + c

(c) is also very small so the fault current peaks out.

The neutral conductor is a separate issue. It is defined as an active conductor and therefore must be sized for continuous full load. In a 3-phase system, if balanced, no neutral current flows. It used to be common practice to install reduced neutral supplies, and cables are available with say half-size neutrals (remember a neutral is always necessary to provide single phase voltages). However the increasing use of non-linear loads which produce harmonics has made this practice dangerous, so for example the current NZ Regs require full size neutrals. Indeed, in big UPS installations I install double neutrals and earths for this reason.

__________________
I love deadlines; I love the whooshing sound they make as they pass by. - Douglas Adams
Register to Reply Good Answer (Score 2)
Power-User

Join Date: Mar 2009
Posts: 130
#4
In reply to #3

Re: Maximum Neutral and Earthing Cable Size

04/27/2009 7:44 PM

Dear BabyGuiness,

Thank you very much for your very GA

Best Regards

Register to Reply
Register to Reply 4 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

aikhh (1); Anonymous Poster (1); BabyGuinness (1); renepang (1)

Previous in Forum: Lifetime of Rechargable Battries   Next in Forum: Suggestions for Capacitor

Advertisement