I have designed the current flow of a 40KVA basic UPS system. The design is based on
The load required - 40KVA at 240V, 60 Hz for 2 Hours.
The available supply - 480V, 60Hz (line to line).
Lowest Battery Discharge level - 25%
DC Voltage level - 125V
The redundant Charger, Bypass Transformer, Static transfer switch, Maintenance switch etc. are not shown in detail in this diagram.
I would like you to provide your valuable comment on this. Once I get your input, I will start my cable selection based on the current values of Case 3. This design reflects some prior recent discussions on UPS.
Note: The bold line indicates the current flow path.
-MS
Good Answers: 73
Re: Need comment on current flow of UPS for different cases
04/27/2009 8:16 AM
Hello msamad,
In reviewing you design, I wondered if you made a common mistake about battery capacity. So, I typed 'battery' in the search all of CR4 box and came up with this most excellent link http://cr4.globalspec.com/comment/40249 that you may wish to read.
I found some of the other hits about batteries very interesting. I am always amazed at the wealth of information available on CR4. I have picked up a lot of useful information and I enjoy looking at the various solutions to problems from such creative people.