MCC Motor Current

04/27/2009 5:54 AM

Dear all,

Please provide me information about the simicode. we have MCC in which SIMICODE is installed but there is no provision of Hard wired Current signal provision to DCS. But our process persons need the current indication of some motors in DCS. How can achieve this. secondly we have profibus in SIMICODE that can communicate to DCS but problem is that for every motor we have seperate profibus. Is there any module available in the market which can change parallel profibus to serial profibus so that by using ony one connector i can communicate all the motors to DCS.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User
South Africa - Member -

Join Date: Nov 2008
Location: Johannesburg
Posts: 295
Good Answers: 12
#1

Re: MCC Motor Current

04/28/2009 1:43 AM

Hi there,

The Simocode is a 'Smart' protection relay for your DOL motor.

As you stated - the Simocode has a Profibus DP interface.

You should never ever have a Star point type connection on Profibus DP. This can cause all sorts of havoc. What you should rather do is sort out your Bus wiring so that all the motors are in serial (i.e. daisy chained). There is a limitation to the amount of nodes (Simocodes) you can put on the DP bus leg - 127.

For a start - www.profibus.com Download the Profibus specifications manuals. This will guide you on the installation requirements for Profibus DP. It will save you a lot of time if you do it right the first time. If you don't - you will regret it as you will pick up spurious interference from incorrect screening/grounding and induction from the electrical cables.

Then goto www.automation.siemens.com You can download the Simocode manual there. It will explain on the diffrent types of configuration and how to set up the data to be passed to and from the Simocode and DCS.

If you have a case where you have multiple motors in different sub stations. You can also look at using Fibre Optic. In this case you will need the OLM (optical link modules) manual from Siemens.

The point to bear in mind - Communications busses must be installed correctly from the onset. If not you will battle for years to get it right.

Just a reminder - Never, ever Star Profibus DP. You will regret it. Not only will you have a lot of noise introduced, but you will have to lower your baud rate so that it it would be faster to walk to the Simocode and take a reading than to use the Bus.

There are devices for parralleling Profibus (Star) - but avoid this. Rather concentrate on getting your bus into a serial (daisy chain configuration) where your flow would be - DP Master - Simocode 1 - Simocode 2 .... Simocode X.

Also make sure that you terminate (use the pull up resistor on the DP connection) the bus at the DP master and at the last node in the line.

Regards,

Craig