an induction motor always getting trip

04/27/2009 11:05 AM

While an induction motor (75 kw) change over to delta main MCCB few times got trip,

after that i can run in delta position.The motor drive a pendulam pulvarizor.There is no problem in mechanical side also motor's winding and insulation values are normal,

also contors good.But some time main breaker tripping some time Main breaker hasn't trip.Please i wanna solve this problem,.....

THANK YOU.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#1

Re: an induction motor always getting trip

04/27/2009 3:54 PM

Circuit breakers operate off a time-current curve, if you have not installed a circuit breaker with the correct curve (such as a D-curve circuit breaker designed for protecting motors and other high inrush current loads) then you will likely experience problem circuit breaker tripping.

Check your circuit breaker is the correct type and current rating for your application.

__________________
jack of all trades
Reply
Anonymous Poster
#4
In reply to #1

Re: an induction motor always getting trip

05/02/2009 4:44 PM

Thank you somuch Mr.........

Reply Off Topic (Score 5)
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#2

Re: an induction motor always getting trip

04/27/2009 6:34 PM

You failed to adequately state how you are starting the motor, but by virtue of your saying it is "change over to Delta" I can assume you are using a Star-Delta motor starting scheme. One of the big problems with Star-Delta as a starting method is exactly what you are experiencing; sometimes if the transition happens at the wrong point in the sine wave, there can be a very high current spike, upwards of 2000 times the motor FLC! There really is nothing you can do about it without changing the starter. Open Transition Star-Delta is really an inappropriate starting method for a high inertia load such as that because during transition, the motor slows down which can exacerbate the problem.

You have 2 choices: 1) Convert that starter to what is called a "Closed Transition Star-Delta", which means adding a 4th contactor and an external resistor bank. the resistors will get red hot during the moment or two they are in the circuit, so you must have free air flow around them to prevent over heating. this makes it a bad choice for dirty environments such as pulverisors. 2) Get rid of the Star-Delta starter and buy a Solid State Soft Starter. it is MUCH better for your motor and mechanical power train components because there is no transition spike of torque, and it will not cause your breaker to trip and cause a loss of production. In the long run, it will end up less expensive to own.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply
Guru

Join Date: Apr 2007
Posts: 577
Good Answers: 10
#3

Re: an induction motor always getting trip

04/28/2009 1:39 AM

What is your incoming MCCB amps rated and it KA rated?

What is your star delta timer setting, how many second you set for it to changeover.

Is your motor direct drive the pendulum pulvarizor or by belts.

We need this information for your answer. Sometime, we do have some problem with the start delta during changeover.

__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....
Reply
Anonymous Poster
#5
In reply to #3

Re: an induction motor always getting trip

05/04/2009 3:54 PM

MCCB 500 AMPS,20 KA RATING

0-30 SEC,Changeover time 15 SEC

Motor direct drive

Reply Off Topic (Score 5)