Laminated Copper Busbars

04/27/2009 10:40 PM

I am currently stacking on a busbar selection problem. I wanna to have 3500A current rating and 65KA/S for short current, and I wanna using 2 layers laminated copper busbars Cu W100mm*T10mm

I have tried forluma A=300*I*[1+0.075(N-1)] W=A/T

and some busbar calculation softwares to calculate, but I am still not sure is W100mm * T10mm enough for 3500A current rating

coz as those old posts said normally 10amp per 1sq mm is ok for single busbar

and some conservational suggestion is 3amp for per sq mm which is too small

so anyone can help to tell me is 2 W100mm*T10mm laminated copper busbars enough for 3500amp?

Many Thanks

Cecil

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#1

Re: Laminated Copper Busbars

04/28/2009 12:04 PM

NEC article 366.23(A) supports maximum 1.55A/mm2 (or 1000A/in2) for bare copper bar.

You also can see http://www.husseycopper.com/Bar/busbarselector.htm

Good luck.

- MS

CR4 Admin: removed broken link

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Reply
Guru
Hobbies - DIY Welding - New Member

Join Date: Sep 2007
Posts: 1601
Good Answers: 58
#2

Re: Laminated Copper Busbars

04/29/2009 6:58 AM

All the formulas you find, are based on the temperature the bus bars will reach under steady state conditions in free air. If those are the end use conditions for your bus bars, then use the tables. If your bus bars oprate in conditions that remove more heat (e.g. forced convection, fluid immersion, etc.) then the formula is not accurate for your conditions. Under those conditions you can operate at higher current.

Reply
Anonymous Poster
#3

Re: Laminated Copper Busbars

04/29/2009 6:57 PM

It's really a matter of physics of current flow and thermal management. One of the great things about copper is it's thermal conductivity. One of the not so great things is that reacts with lots of things given its atomic structure, such as oxides and ionics.

Both of which result in degradtion, therefore you might want to consider immersion and or plating. I would look into immersion since you would get the biggest bang for the buck. Of course that approach must be consistentwith your physical/logistical constraints.