Can any one explain the Importance of station transformer in the power plants and Importance of GCB(Generator circuit breaker)? If GCB present then station transformer (ST) is not usefull? Please explain both
Re: GCB versus ST
04/29/2009 6:11 AM
Dear Mr. Rajesh,
Station Transformer (Any Transformer) meant for Distribution (means you can use it for HIgh voltage or Low voltage and for step down or step up application). The Circuit Breaker meant for Protection.
So both are impartant in a electrical netwrok.
Re: GCB versus ST
04/29/2009 7:31 AM
ST is used to supply power to certain critical auxillary load (Certain loads should be in operation even when the power plant is not fully in operation) in a power plant....
GT is a protection device for generator
Re: Generator Circuit Breaker vs. Station Transformer
06/15/2009 4:31 AM
both answers are wrong...yes we can eleminate the ST by using the GCB. but most of modern power plants for back up purpose ST also using
06/30/2009 4:26 AM
function of stsation trnaformer in power plant is which supplies the power during the initial start up and black out condition
yes there is relation between the GCB and ST if GCB is present then in that case we can take the power for initial strt up by opening the GCB provided unit should be connected to the grid
07/28/2010 6:47 AM
GCB and Station transformer can be substitute of each other. station transformer supply power to the auxillaries of power plant which are essential to start the generation.
in case of GCB, of initial charging of auxillary the GCB is open and power is suply to axillaries through auxillary transformer and once the voltage reach to required value through synchronisation it is close.
whereas in case of station transformer it supply directly to the station load.
07/28/2010 7:26 AM
Ya I know but in the operation point and performance point of you which one is best and is there any effect on generator if GCB is used directly connected from Switchyard.
10/07/2010 2:49 PM
I would like to mention that GCB is used for two purposes :
1. to protect Generator transformer
2. to enable the unit auxiliary transformers to receive power directly from the grid during plant startup
3. it reduces the burden on the station transformer and in some cases station transfomer can be completely eliminated