Earth resistance

04/30/2009 2:00 AM

what would be the standard earth pit resistance for electrical equipments. kindly post the references of international standards.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: Earth resistance

04/30/2009 2:32 AM

Earth Pit Resistance should be typically lesser than 2 ohms when connected to earth grid and should be lesser than 4 ohms when test pit is not connected to grid

However this may not be a complete information and may sometimes vary to higher level depending on design

Some international standards that can be ref DIN VDE 0141, ANSI/IEEE Std 80

Regards

Register to Reply
Anonymous Poster
#2

Re: Earth resistance

04/30/2009 2:36 AM

Standard Earth pit resistance for electrical equipments should be less than one ohm.

Sanjeev Gupta

Register to Reply Off Topic (Score 5)
Power-User

Join Date: Nov 2008
Location: India
Posts: 333
Good Answers: 6
#3

Re: Earth resistance

04/30/2009 2:53 AM

dear,

pl. refer IS 3043 .

Earth pit resistance of Each electrode required generally < 1 Ohms.

But, for rocky area, tolerable up to < 5 Ohms.

If you find different results, then, you need to find out the solutions / remedies for the same. to get better earth results .

Infact, with the advancement of electronics, the results required are more stringent then the guide lines depicted in the IS standards.

__________________
Exploring the Science of Electricity