Transformer not allow operate more than 50% load

05/02/2009 10:09 AM

Hi all

I am working in an Oil & gas company having 2 units 40MVA, 66KV transformer and the Tie breaker is always keep close. Why the PE does not recommend to operate above two transformers more than 50% load. If I operate the above two transformers more than 50% load,what will happen? Please advise me.Thanks

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Power-User

Join Date: Dec 2006
Posts: 346
Good Answers: 6
#1

Re: Transformer not allow operate more than 50% load

05/02/2009 5:30 PM

hi all; if one went bad, the other could pick up the total load.? perry

Reply
2
Associate

Join Date: Feb 2009
Posts: 34
Good Answers: 4
#2

Re: Transformer not allow operate more than 50% load

05/03/2009 3:47 AM

It is obvious that someone has decided to operate at N-1 so that if you lose 1 transformer the other take the full load. This is acceptable but in normal power systems you would tend to run the transformers at about 70% and if you need to cover all the load with one you can generally overload the transformer to 120% continuously. You will accelerate the aging & you will need to look at what you need to drop of or shed in the load whilst the other Tx is repaired or replaced.

Having said that the bus-tie, busbar rating & protection system may constrain the load that you can operate at. You need to check this as I have seen some places where they put in larger Tx that the bus current rating & set limits. Not good practice but it does happen.

You need to do some research into the history of the design to find out why.

__________________
Murphy was an optimist....
Reply Good Answer (Score 2)