Generators and Excitation Protection

05/06/2009 2:27 AM

We have 55MW Generator unit. It was tripped with under excitation protection. What is under excitation protection ?. What is its scheme and relay settings?. Generator output is 11 kv.

RBN

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User

Join Date: Sep 2007
Location: Sheboygan, WI USA
Posts: 372
Good Answers: 13
#1

Re: Generators and Excitation Protection

05/06/2009 11:07 PM

Have you tried to reset the under-excitiation relay and restart the unit ?

What results ?

Is the exciter a rotating or static ? Manufacturer and model number ?

What vintage is the relay ? Manufacturer and model ?

What is the prime mover ?

Is the unit on a grid or isolated ?

How big is this generator relative to the grid size ?

If a small grid, biggest load ?

More detail will help provide a better answer to your question, and at some point you may answer yourself.

__________________
"I believe we are masters of our lives - we hold all the cards and it is up to us to use them right." Vesna Vulova - survived 33,000ft fall
Register to Reply
Power-User

Join Date: Dec 2007
Location: Brasov, Romania
Posts: 255
Good Answers: 7
#2

Re: Generators and Excitation Protection

05/07/2009 2:19 AM

Main reasons for excitation protection to trigger is shortcircuit in excitation winding and maybe overheating of the excitation. The electric fault may occur as ground fault for one winding in which case you need differential protection for rotor; the other case is fault between two rotor windings, triggered by overcurrent protection.

the schemes are just like ordinary overcurrent and differential protections.

__________________
The time is ......now
Register to Reply
3
Active Contributor

Join Date: Sep 2008
Location: Lusaka, Zambia
Posts: 10
Good Answers: 2
#3

Re: Generators and Excitation Protection

05/07/2009 2:21 AM

The excitation system is the dc circuit supplying the generator rotor to maintain the magnetic field i.e. flux. The rotor flux and stator flux interact to produce a resultant flux. If the rotor is over excited, no reactive current will be drawn from the stator (connected to grid) i.e. sending reactive power to the grid and if under excited, the balance of reactive current to maintain the flux will be drawn from the grid i.e. drawing reactive power from the grid. There is therefore a minimum excitation current that the generator must be supplied with to maintain this flux and varying the magnitude of excitation current therefore also controls the power factor of the generator.

Under excitation protection on small units will merely be an under current relay monitoring the excitation current while larger units will have more elaborate schemes responding to the power factor which will tend to leading as the excitation reduces. A loss of excitation also results in the generator terminal voltage reducing with stator current increasing (drawing current from grid to maintain flux) causing a decrease in impedance as viewed from generator terminals. Other protection schemes respond to this change in impedance.

S.L

Register to Reply Good Answer (Score 3)
Commentator

Join Date: Mar 2009
Posts: 57
#6
In reply to #3

Re: Generators and Excitation Protection

05/07/2009 1:35 PM

Dear ZM

Thanks to your good comment.

BRN

Register to Reply
Associate

Join Date: Apr 2009
Location: DR Congo
Posts: 31
Good Answers: 2
#4

Re: Generators and Excitation Protection

05/07/2009 8:55 AM

Answer of ZM eng is absolutly true. This is more theoritical answer & explaining exactly what is going on in the gerertor.

Practically,

If you are running generator in parallel with Grid. In that case, excitation governs pf of the Generator.

If you are running Generator in isolation then Excitation governs Terminal Voltage.

Now I am assuming your generator is running with Grid. Normally, when it is running with grid one contact of Grid breaker is wired in AVR. It gives comand to AVR for controlling pf not terminal voltage. This pf is being set by opertor on AVR by some variable port or any other mathod as per AVR. Now By chance that Grid breaker contact to AVR goes off, but actually Generator is running with Grid. in that case AVR will shift in isolation operation mode. & it will vary excitation current in such that it maintain terminal voltage as 11 kV. Now at that time if Grid voltage is more then 11 kV, say 11.3 kV. Hence AVR will reduce excitation current but actually teminal voltage can not reduce COZ it is running with Grid. Hance pf will go toward 1 & then to leading side & ultimate excitation current will reduce very low & it may cross beyond Generator excitation stability curve. In this case your excitation monitoring relay will operate & trip the generator.

This is only one type of case. Tell more about youe system then one can give more reasonse for tripping.

Register to Reply Score 1 for Good Answer
Commentator

Join Date: Mar 2009
Posts: 57
#5
In reply to #4

Re: Generators and Excitation Protection

05/07/2009 1:31 PM

Thanks to your reply.

The generator is connected to Grid. We have 3 Generators running in the Power House and all the Generators are connected to the Grid. The frequency is 50 Hz. Capacity of each generators are 55 MW each. The excitor is static excitor system. This is a hydroelectric Plant.

The machines are normally running with pf = 1 and MVAR = 0. Sometime the load despatch centre is requesting to incrase the MVAR. In what cercumstance MVAR is required for the Grid?. How we can control MVAR ?.

Can you please discribe the relation between MVAR, pf, terminal voltage and excitation current and voltage ??.

BRN

Register to Reply
2
Power-User

Join Date: Aug 2007
Location: Heilonjang China. 2 blocks from you
Posts: 109
Good Answers: 5
#7
In reply to #5

Re: Generators and Excitation Protection

05/07/2009 7:16 PM

Byjuram theoretically ZM eng is absolutly right and practically ajay Patel is also right.

From ZM eng's statements, If the rotor is over excited the generator will be sending reactive power to the grid, and if under excited, the generator will be drawing reactive power from the grid,reactive power is measured as Mvar.

Now your generator is connected to the grid and when the Local control center tells you to increase on the Mvars that means the grid voltage is low compared to the standard voltage i.e if your grid voltage is 132Kv and it drops to say 127Kv that means your generators are drawing reactive power from the grid thus you have to over excite you generators to meet the standard grid voltage also if the local control center tells you to reduce on the Mvars that implies the grid voltage is high from the standard voltage i.e over 132Kv in this case you have to reduce on your generator excitation (under excite). If the grid voltage is high there is going to be a possibilty that the customer's voltage is also going to be high beyond normal and vice verser.

Practically the relation between excitation and power factor has been mentioned earliar but now let me give you the rest

High Mvars will give you high generator terminal voltage and high line or grid voltage and

Low Mvars will give you low generator terminal voltage and low grid voltage.

How ever you at the power station have only one way of controlling the system Mvars the local control will tell you to under excite or over excite your generators and if your generators are at the maximum then the local control center will find an altenative by puting in capacitor banks.There are other methods of controlling system voltage.

Its amazing that your machines run at 0 Mvar, that implies that the sator or terminal voltage is 0Kv, field current is 0A and thus power factor is 1, I think at your operator station you will only see these figures when the machine is at standstill but when its on load then you wll not have this.

I sugest if your system is automated and you monitor generator field current, p.f, Mvar and stator voltage, take note of these when the generator is being syscronised and loaded, as you load the generator MW you will also be increaseing on the Mvar to avoid triping on under excitation when the generator is fully loaded.

Hope this helps.

__________________
poy
Register to Reply Good Answer (Score 2)
Commentator

Join Date: Mar 2009
Posts: 57
#10
In reply to #7

Re: Generators and Excitation Protection

05/09/2009 12:29 AM

Dear Waco,

I need your comment about Mr.Ajay's views.

Rgds

BRN

Register to Reply
Associate

Join Date: Apr 2009
Location: DR Congo
Posts: 31
Good Answers: 2
#8

Re: Generators and Excitation Protection

05/08/2009 10:17 AM

Dear Byjuram,

As you said that you are running Generators at unity pf, & your load is also being control by LDC, I can conclud that you are Power Generating Plant & Feeding your all Generation to Grid.

It is really surprizing that you are running your generators are 1 pf. Be careful, you are near to leading pf. As soon as your excitation current will reduce little your generator will be in leading pf. And please see Generator stability curve given by your generator manufacturer. In leading operation, it may possible that your roator will start heating. It is always better to run Generator in lag.

That's why we provide loss of excitation relay. We can also say that it is reverse reactive Power Relay. Both are doing same function & Relays are connected to Statos Voltage & Stator Current, not on DC Field side. Please check your relay which was operated, whether it is connected to Excitation side (Rotor side) or Stator Side & let me know.

Please let me know, whether your generator trips frequently on excitation fail?

I am in hurry, I will wite some thing more on this.

Ajay

Register to Reply
Commentator

Join Date: Mar 2009
Posts: 57
#9
In reply to #8

Generators and Excitation Protection

05/09/2009 12:26 AM

Dear Mr.Ajay

Thankyou for your reply

You are right, the Generators are connected to very huge grid. We have total 6 generators with 55 MW for 5 generator and 60 for one generator. Out of 6 only three in service and total load is 55+55+60 = 170 MW.

Generation voltage is 11KV. Stepup transformers are using to stepup the volttage to 220KV. The generators are running at pf=1. I didn't noticed any variation in pf and MVAR. When we reduce the load of the machine, the MVAR is slightly varying but within seconds it came to zero. We dont have capacitor back in the generating station.

Mr.Ajay - What are the additional parameters or measurements required for you to analyse my situation. Write me. I will provide complete information.

Rgds

BRN

Register to Reply
Power-User

Join Date: Aug 2007
Location: Heilonjang China. 2 blocks from you
Posts: 109
Good Answers: 5
#11
In reply to #9

Re: Generators and Excitation Protection

05/09/2009 11:08 AM

Byjuram

As ajay said i know your generators are on grid but running your generator close to unity p.f is not o.k,maybe thats why it trips. Have you been runnig this generator under these conditions for a long period? And are all generators behaving the same, if not all then am of a view that since you have a very small variation between the Excitation current and the Mvar you consider checking the tap positions of your generator transformers. I think thats why you manage to run your generators at 0 Mvars, of late we had a similar situation when one of our generators stator voltage is around 11.4 Kv with our referance Mvar at 3Mvar, so we managed to get rid of that by varring the tap position of the generator transformer to much the other generator transformers, but i do not remember which tap position was the calprit generator transformer but what i remember is that the other generators are at tap position 2.

Dose the generator trip out during a system disturbance? Also try to varry the excitation or Mvar referance point but don't use the load referance, then note the field current and the stator voltage. Since you run it at referance 0 Mvars try to adjust it to 3 or 5 and note the field current and the stator voltage, Do the same to another generator.If there is a big varriation then consider changing the transformer tap position.

Note:

If you increase Excitation or Mvar

-field current will increase

-Stator voltage will increase

Power factor moves away from Unity.

And the reverse is true. So at 0Mvars that's why you have Unity p.f. The generator will run fine because other generators on the system are providing the reactive power needed by the system and your generator will tend to draw part of this to maintain it's self but if the generators on the system are under excited or more inductive loads are put to the system, they will reach their maximam point that they will not supply any more reactive power thus your generator to be under excited because it's excitation was being supported by the grid, thus it will trip out.

And if you reduce LoaD (MW referance)

- field current will reduce

- Power factor moves further away from Unity

__________________
poy
Register to Reply
Commentator

Join Date: Mar 2009
Posts: 57
#12
In reply to #8

Generators and Excitation Protection

05/09/2009 1:07 PM

Dear Ajay & Waco

The following are details of my system

1. Unit #5 machine running with 55 MW, Iexc=539 A, Uexc=139.3 V, PF=1, MVAR = 0, MW=55.1, F=50.3 Hz, Speed=502 RPM

2. Unit #6 machine running with a reduced load 30 MW (Actual capacity is 60MW), Iexc=602.8A, Uexc=110.6V, pf=1.0, f=50.2, speed =501 RPM

3. All machines are connected to Grid

4. I understood from our relay testing team, the excitation setting is done as below

a) Rotor angle 75 - Stage 1

b) 14 Amps DC current measurement. Transducer 4-20 mA - Stage 2

Instantaneous trip.

5. The excitation system is :

Type : static Elin-Thyre 5 IEEE 421

Rated voltage = 250 V

Rated current = 800 A

6. Exciter Transformer

438 KVA, Volt HV 11000, LV 350, Current HV 22.98, Current LV 722.53

Phase 3, f=50Hz, Dy5.

So the excitation setting is based on the rotor angle for the stage 1 and DC excitation current for stage 2.

The excitation system here is keeping the power factor unity. If any reduction in load the MVAR will increase but within seconds it will become zero. We are using SCADA system to change the MW & MVAR if the LD insists.

I hope you got information about our system. Please comment based on this information.

The generator is not tripping frequently with under excitation protection.

Rgds

BRN

Register to Reply
Commentator

Join Date: Mar 2009
Posts: 57
#13
In reply to #8

Generators and Excitation Protection

05/16/2009 4:51 AM

Dear Ajay,

Please reply based on my previous mail.

Rgds

BRN

Register to Reply
Power-User

Join Date: Sep 2007
Location: Sheboygan, WI USA
Posts: 372
Good Answers: 13
#14

Re: Generators and Excitation Protection

05/16/2009 9:22 AM

Unity PF is when the generator excitation is correct to produce minimal amperage and HEATING in the generator windings, as the generator is producing KW only. Observe this when the generator is online, vary the excitiation up and down slightly and you will see that the generator amp meter "dips" at unity PF, the KVA meter will also read zero. This is how to do a metering check to verify proper wiring.

Producing KVA to have a power factor other then unity, does take power and does create more current flow in your generators windings which produces more HEAT which is cumulatively detrimental to the winding insulation, requires more HVAC to remove the heat, thus reducing efficiency, and may limit the generators ouput during hot weather.

So unless you are the utility it is always in your best interest to run at UNITY PF to reduce heating in the generator windings. I have started 15 hydro plants and always set the Auto Voltage Regulator/Power Factor Controller to run at unity PF.

One thing you may need to look into is the PF after your station transformer to make sure that the plant out at the utility metering is metered at 0 KVAR.

Thru the course of questions and statements some of the questions I initially asked have been answered, regarding the Loss of Excitation relay operation.

But you still don't know why it operated if I am following the string ?

__________________
"I believe we are masters of our lives - we hold all the cards and it is up to us to use them right." Vesna Vulova - survived 33,000ft fall
Register to Reply Score 1 for Good Answer
Register to Reply 14 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Ajay Patel (2); byjuram (6); CoronaCameraMan (2); nikolay (1); olivinak (2); zm_eng (1)