FCMA neutral soft starter
05/09/2009 9:40 AM
hi in my company last month a soft starter was burnt due to malfuntioning of the thermostat. rating of the starter is: 475kW , 3300 volts, 50 hz driven equipment -fan 2 thermostat of rating 30-85 deg.C are in series & it is stem type. plz let me know other method of avoiding such occurance in future , is other type of some electronic thermostat is available if yes than plz specify its rating and caliberation. And what can be the best place to place the thermostat in the panel , for the best possible monitering.
Good Answers: 804
Re: FCMA neutral soft starter
05/09/2009 6:37 PM
Being that only one company in the entire world makes this FMCA starter, they are the only ones who can answer that question. This points out the concern I have expressed to people on going with such a unique product.
05/11/2009 6:33 AM
hi
aleast plz give some advice man , i am totally new to this starter.
looking forward for your precious reply..
thankyou.......
05/11/2009 9:19 AM
JRaef is correct. There is only one supplier for these and you have to go to them for advise on reconfiguration.
I have only dealt with them once and it was neither quick or pleasant.
Rick S.
Very funny Scotty, now beam down my clothes!
05/13/2009 10:55 PM
Which part of your soft-starter burnt and what is your driving load (the power KW of your fan).
05/14/2009 2:37 AM
hi simon wan ,
the core of the fcma was burnt . As far as i have investigated the thermostat has caused such thing . Plz let me know about any electronic thermostat which i can put in service .
the rating of motor is 475kW & 33kV.
05/14/2009 3:45 AM
I think the actual problem of your soft-starter failure is not the thermostat problem. Thermostat does not cause the soft-starter to fail or breakdown. Thermostat is to monitor the temperature of the motor winding (if you install it to the motor) or in other case to monitor your soft-starter panel temperature (if your soft-starter has a thermostat). Any temperature that over the set temperature of the thermostat will trip your electrical system for safety.
By the information that you have given to me, it is seem that, you are loading your soft-starter more than 100% to 120% capacity of your soft-starter.
Your soft-starter is rated at 475KW at 33KV and your motor power is also at 475KW at 33KV. In general, we always install one step higher capacity of the soft-starter for the rated motor power (KW). For example, if I am using 475KW motor, my soft-starter will be a step higher, something like 520KW soft-starter.
This is to ensure that during the motor is in operation, there is always a buffer zone for the soft-starter to play around with the extra power it have. There are something that you don't see or notice during the operating of your motor.
For instance, if your voltage drop from 33KV to 30KV or your fan may slightly jammed during operation, your motor current will increase and thus will cause your soft-starter and your motor temperature to increase.
We have been using so many soft-starter in here but so far we don't have these problem with the thermostat problem.
There is a lot of electronic temperature sensor and controller in the market that you can used. You can use PT100 temperature sensor and most of the controller are universal where you can use to replace your thermostat problem.
07/18/2009 12:24 AM
I think it's better that you consult the provider.
frequency inverter, soft starter, servo motors, ac drives