What is chiller interlocking?
On what basis we can select the chiller?
What is chiller configuration?
Re: HVAC Problems and Chiller Questions
05/15/2009 6:51 PM
For example, chilled water pumps, condenser water pumps, and cooling towers are usually interlocked with chiller operations so when chiller runs they all run
Select the chiller or chiller combination that meets a required load at minimum cost
Chiller configuration is when chillers are piped in series or parallel, However series configuration is rarely used because it requires constant flow rate at all times
05/16/2009 7:24 AM
thank you for your answer