Anonymous Poster

MPCBs vs. MCBs

05/15/2009 1:40 AM

Major difference between MCB and MPCB

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Apr 2007
Posts: 577
Good Answers: 10
#1

Re: MPCB VS MCB

05/15/2009 4:12 AM

What is MPCB ?. It is MCCB..

__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....
Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#2

Re: MPCB VS MCB

05/15/2009 2:13 PM

If by MPCB you are meaning Motor Protection Circuit Breaker, the difference is in the adjustable trip settings. MCBs are not adjustable; you buy them in fixed values, i.e. .6A, 3A. 16A etc. In addition, the magnetic trips are fixed by virtue of the "Curve" type selected at purchase. S for instance, the "B" curve is not typically used for motors where the "D" curve is, but a D curve may not adequately protect more sensitive equipment.

An MPCB has adjustable trip settings within a range typically seen in motor circuits so that you can more closely define the trip characteristics you want to not only protect your motor, but also to avoid nuisance tripping.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply
Guru

Join Date: Apr 2007
Posts: 577
Good Answers: 10
#3

Re: MPCBs vs. MCBs

05/15/2009 8:18 PM

If you are talking about "motor protection circuit breaker" then Mr.JRaef has the answer. I don't know what brand you are using but down here we call "Thermal-magnetic and magnetic circuit-breakers" Here is the link to it.

We don't call MPCB. It confusing.

http://www.schneider-electric.com/corporate/en/products-services/automation-control/products-offer/range-presentation.page?p_function_id=27&p_family_id=282&p_range_id=1446

__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....
Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#4
In reply to #3

Re: MPCBs vs. MCBs

05/17/2009 3:17 PM

Please see the posting http://cr4.globalspec.com/thread/33001#comment345618. It has a answers for this question.

-MS

__________________