AC & DC

05/17/2009 3:32 AM

hi gents,

there is something i saw and it start turning in my mind and i would like to get explaining from you guys if you dont mind.

we do test for over current relay of GE752 DC generator, we do it by shorting the output leads +,- coming out from the generator which passing through DC contactor which will be off when the over current relay function.

we see the amps meter readings and increase the output from the generator untill the amps readings reach 1300DC amps.

my question is why it goes ok when we short DC currents? can we do the same for AC volts generator?

is that because the power goes in one direction from + to - and back to the generator 'one direction' and so on? while on AC it goes from phase A then B phase comes positive before A phase comes negative and the two lines become positive and cause short?

your help is appreciated

thanks

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Canada - Member - Specialized in power electronics

Join Date: Feb 2008
Location: Montreal, Canada.
Posts: 1372
Good Answers: 80
#1

Re: AC & DC

05/18/2009 9:23 AM

You should be able to use a short circuit test to set the overcurrent protection for an AC generator.

The problem is that there are usually more protections to set on an AC generator. Some other method must be used to set the other protections like phase imbalance, reverse power, third harmonics... Once you have a setup that can simulate those complex situations, you might as well add the over current and save the trouble of doing a short circuit test.