Ramifications of NOT Grounding a Vehicle

05/19/2009 10:16 AM

At hand is a system of electronic equipment in a vehicle that is powered either by internal inverters or from an outside source (i.e. generator). It is all single phase, 120 VAC.

In vehicle mode (inverters) where the vehicle is stationary, would it be prudent to ground the vehicle for at least safety reasons (i.e. fault condition such that a person touching the vehicle standing on the ground could be exposed to lethal electrical potential)?

In the external power source mode, would it be prudent to ground both the source (generator) to earth ground and the vehicle?

In either mode (external power or vehicle inverter power), what would be expected to happen in the event of a direct or indirect lightning strike if the vehicle is NOT grounded?

My thinking for external power is that the lack of an earthen ground is dangerous in that the combined system of generator and vehicle is a giant floating chassis whereby energy can be coupled onto the chassis presenting electrical potential between this chassis and earthen ground. A person standing on ground could then be exposed to this potential energy.

Thoughts?

__________________
This moment is as it should be.
Also posted in: also posted in Transportation
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User
Hobbies - HAM Radio - New Member

Join Date: Oct 2008
Location: Houston, Texas
Posts: 252
Good Answers: 5
#1

Re: Ramifications of NOT Grounding a Vehicle

05/19/2009 1:46 PM

Not my field but, It is quite common to use inverter power sources in mobile equipment. The impossibility of grounding a moving or frequently moved structure essentially means that any ground used will be simply to the containing structure, vehicle body, frame etc. I worked for a geophysical company for a while and we had equipment powered by generators, battery powered inverters and even thermal generators. If the power source was grounded to anything, it was grounded to the vehicle frame. If the power was to be used outside the vehicle to provide power to other vehicles, trailers, and so on, in a fixed location, there was a ground drilled in and the equipment was grounded to a common point. We often used ground fault protection on circuits that were powering portable equipment like core drills, cooling fans and such stuff.

Having explained the practice I observed, I have no idea what the code calls for in this case.

Have FUN!
TT3

__________________
If the software can detect, compensate, avoid, or correct an anomalous condition in the system, it is, by definition, a software problem-regardless of the root cause. In the long run, for most classes of problems, it is cheaper to fix it in the SW
Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#2

Re: Ramifications of NOT Grounding a Vehicle

05/19/2009 9:16 PM

There are several different possible answers to your question. But first, some questions.

How do you switch between the sources?

Do you use a transfer switch of some kind? If so, how many poles on it?

You need to see if the neutral, or the identified conductor (using Canadian code language), from the inverter (is there more then one?) is tied to the case of the inverter. See if there is continuity between the neutral and the case and let me know.

How much power in watts are we using? Is the inverter powered by the vehicle alternator or batteries or a combination of both? What is the input voltage to the inverter(s)?

Any RF systems involved in this rig?

Interesting question... to give you proper advice, the asked for information is needed.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Guru

Join Date: Feb 2008
Posts: 638
Good Answers: 45
#5
In reply to #2

Re: Ramifications of NOT Grounding a Vehicle

05/21/2009 11:47 AM

Switching is done automatically by the inverters. The inverter senses loss of external power and switches to inverter mode.

RF-yes; primarily receiver systems (UHF, VHF) and one microwave transceiver (25W RF power out 11 GHz).

There are 2 inverters each running in parallel to the vehicle's alternator/battery 24VDC system. Each inverter provides on-the-order of 2500W of power to separate distribution circuits (done inside of a power distribution box with current protected swithes to various branch circuits.

One inverter mode is Internal Neutral-to-Ground Switching (Battery .Inverter. Mode)-The AC output neutral is connected to the chassis ground by an internal relay when the inverter is operating from the batteries, thus creating a neutral to ground bond within the inverter.

A second inverter mode is External Neutral-to-Ground Switching (AC .Shore Power. Mode)-The inverter's internal relay opens and removes the ground from the neutral conductor when the vehicle is connected to an external AC power source. The neutral is connected directly to the output neutral thus providing the neutral bond at the external AC source.

__________________
This moment is as it should be.
Register to Reply
Associate

Join Date: Jul 2007
Location: Spokane Wa. USA
Posts: 29
Good Answers: 2
#3

Re: Ramifications of NOT Grounding a Vehicle

05/20/2009 1:03 AM

Grounding doesn't hurt, you can't be to safe. That said, you shouldn't have any problems with the built in inverter as this is essentially a floating AC power supply with the neutral and ground circuits returning to the vehicle frame. The external power generator also needs to be grounded to the frame. The vehicle is insulated from the earth ground by its tires, so to prevent static build-up you should have at least a dragging strap or better yet. when you stop to use your equipment use an actual grounding rod. This is especially true if you're running any kind of transmitter.

Register to Reply
Guru

Join Date: Feb 2008
Posts: 638
Good Answers: 45
#4
In reply to #3

Re: Ramifications of NOT Grounding a Vehicle

05/21/2009 11:34 AM

Ahh, an interesting observation about ground and neutral on vehicle frame. The wiring infrastructure in this case is that neutral is isolated (with the intent that it ties together at the source when using an external source).

This begs the question; Would it be prudent to implement a method by which to tie the neutral and ground together when in the inverter or vehicle power mode?

Tony

__________________
This moment is as it should be.
Register to Reply
Guru

Join Date: Feb 2008
Posts: 638
Good Answers: 45
#6
In reply to #4

Re: Ramifications of NOT Grounding a Vehicle

05/21/2009 3:54 PM

Correction

Neutral to ground is switched-see post #5

__________________
This moment is as it should be.