Magnetic Contactors and Single-Phase Power Supplies

05/21/2009 6:23 PM

can 3 phase electrical magnetic contactor be operated in single phase power supply?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User
New Zealand - Member - Kiwi

Join Date: Oct 2007
Location: Christchurch, New Zealand
Posts: 328
Good Answers: 29
#1

Re: electrical contactor

05/21/2009 8:39 PM

Yes, it can. It is commonly done where larger lighting loads are switched. The single-phase feed is commoned on the 'L' side of the contactor, and each connection on the 'T' side of the contactor feeds a separate set of subcircuits. Just make sure that the coil is of the correct voltage rating.

__________________
paulusgnome
Reply Score 1 for Good Answer
Participant

Join Date: May 2009
Posts: 2
#4
In reply to #1

Re: electrical contactor

05/21/2009 9:21 PM

Thanks for the information.

Reply
Guru

Join Date: Apr 2007
Posts: 577
Good Answers: 10
#2

Re: electrical contactor

05/21/2009 8:54 PM

"can 3 phase electrical magnetic contactor be operated in single phase power supply?"

Can you please re phase your question again?

What do you mean by 3 phase electrical magnetic contactor be operated in single phase power supply?

Are taking about, the energizing of the magnetic contactor coil using single phase supply or are you talking using the contact point of the contactor for single phase load usage.?

Your question is not clear

__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....
Reply
Participant

Join Date: May 2009
Posts: 2
#3
In reply to #2

Re: electrical contactor

05/21/2009 9:19 PM

Thanks for your immediate response. My question is, we already have a three phase magnetic contactor can we energize it using sigle phase supply?

Reply
Guru

Join Date: Apr 2007
Posts: 577
Good Answers: 10
#5
In reply to #3

Re: electrical contactor

05/21/2009 9:31 PM

Your question is still not clear.

I presume that your 3 phase contactor coil is rated at 415v and you want to use single phase voltage of 240 v to energise your contactor. Am I right.?

Well the answer is NO. Your single phase voltage is not able to energize your 415V contactor coil. BUT....

You can change your 3 phase contactor coil rated 415v to the single phase 240v coil. Most of all the contactor in the market, the contactor coil is interchangeable to suite the voltage requirement.

__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....
Reply
Power-User

Join Date: Sep 2008
Location: Jakarta, Indonesia
Posts: 104
#6
In reply to #5

Re: electrical contactor

05/22/2009 2:53 AM

Nice respond Simon Wan,

additional question is :

when we are talking about 1 phase. is it

1. phase to neutral (neutral from center of Wye): 415 / √3 = 240 volt , or

2. phase to neutral (neutral from center of one side of delta) : 415/2 = 207 volt, or

3. phase to phase : 415 volt

R - S : 415 volt

S - T : 415 volt

R - T : 415 volt

I

Reply
Guru

Join Date: Apr 2007
Posts: 577
Good Answers: 10
#7
In reply to #6

Re: electrical contactor

05/22/2009 3:34 AM

Yes. When we say 1 phase or Single phase supply, we will consider as a phase to neutral power supply (for the case of star point transformer) in which for phase to neutral (neutral from center of Wye): 415 / √3 = 240 volt

But if we are talking about, 1 phase or Single phase supply for the Delta type, then actually, the phase voltage = Line voltage = 415 volt.

__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....
Reply
Anonymous Poster
#8

Re: Magnetic Contactors and Single-Phase Power Supplies

09/11/2009 7:34 PM

yes because only magnetic contactor is 3 phase and the coil of magnetic is 220 yes can operate. josetech_@hotmail.com

Reply
Reply to Forum Thread 8 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); elect-ok (1); josejordan_fernandez711 (2); Paulusgnome (1); Simon Wan (3)

Previous in Forum: Research and Development in Electrical Engineering   Next in Forum: PLCs vs. Industrial PCs

Advertisement