Deluge Line Philsophy

05/22/2009 5:38 AM

Hello,

We got a deluge valve operated by a Solenoid ( With Interlocks for Instrument air Pressure low-- )

What should be the operating philsophy ( Energise to Trip Or Deenergise to Trip)

Package Vendor has proposed for De -energise to Trip, Philsophy

Somewhere i read all( not able to recollect the source) all Fire And Gas & Associated system Should be Energiise to Trip

Kindly advise on the Trip Philsophy ,for Deluge and Fire and Gas system

Regards

Jose John

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: Deluge Line Philsophy

05/23/2009 12:24 PM

Hello Jose It is absolutely fine to have de-energise Solenoid to have deluge operated. Deluge system works with counter balancing philosophy and has water pressure on both sides with additional air pressure on one side to keep the deluge closed. As soon as air pressure is removed, the water presssure on one side will open the deluge as thne area on that side is bigger than the area on other side. Hope I am bale to clarify cheers

Register to Reply
Guru
Belgium - Member - New Member APIX Pilot Plant Design Project - Member - New Member

Join Date: Aug 2006
Location: Glabbeek, Belgium
Posts: 1480
Good Answers: 28
#2
In reply to #1

Re: Deluge Line Philsophy

05/25/2009 2:22 AM

What you explain is the dry alarm valve: a balance of low air pressure and high water pressure.

But indeed it is normal to use normal open solenoids in this case.

It is even mandatory as the valve is to be used in a security system.

__________________
"Here we are now, entertain us"
Register to Reply
Power-User
South Africa - Member -

Join Date: Nov 2008
Location: Johannesburg
Posts: 295
Good Answers: 12
#3

Re: Deluge Line Philsophy

05/25/2009 2:30 AM

Hi there,

We use de-energise to trip on deluge systems - fail safe. The control valve is also fail open.

In other words the instrument air keeps the valve closed while the solenoid is energised.

So, if you loose power, and/or instrument air the deluge valve would open. This is done because you might have a fire that burns your signal cable.

We also have a manual overide on our solenoids for testing purposes. We have mechnical block valves upstream of the deluge control valve to isolate if needed.

Regards,

Craig