Anonymous Poster

Short Circuit Current

06/17/2009 7:01 AM

Dear all, We are currently supplying electrical starter panel for one of the project. Specifications says busbar to with stand 15KA for 1 sec however supplier is confirming 50KA for 1/2 cycle. can any one give me clear idea which one is better. Thanks in advance Shashidhar

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#1

Re: Short circuit current

06/17/2009 7:26 AM

The heating effect is given by the term I2 x t, where I is the current in the conductor and t is the time.

For the first case, I2t = 152 x 1 = 225

For the second case, at 50Hz, I2t = 502 ÷ 100 = 25 (and it's even smaller for 60Hz).

So the 15kA for 1 second gives about five times as much heat.

If you want to meet the spec, don't take your supplier's offer.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Reply Score 1 for Good Answer
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#2

Re: Short Circuit Current

06/17/2009 8:10 PM

Every piece of electrical apparatus has a short-circuit withstand rating. It can carry only so much current for so much time before it is damaged. For example, bus duct may have a short-circuit rating of 50,000 amperes for three cycles. If 75,000 amperes were to flow through the bus for three cycles, it might be damaged. Or. If 50,000 amperes flow for 12 cycles, it might also be damaged. Nationally Recognized Testing Labs such as UL often take short-circuit withstand ratings into account when they test products. In the example above, the short circuit test on the busway would likely include the overcurrent device. So, the busway might be tested at 100,000 amperes when protected by an 800 ampere Class L fuse. If the busway passed the test, it would be marked as suitable for use on a circuit capable of delivering 100,000 amperes when protected by a Class L fuse of no greater than 800 amperes.

So where does that leave you. A fault current of 15 ka for 1 second is not likely. It will be more like 50 ka for 1/2 or 1 cycle at the main switch. Depending on the protection, the OC device should interrupt the fault in less than 1 cycle. You need the fault current level at the location of you equipment to size it correctly.

Reply Score 1 for Good Answer
Commentator

Join Date: Feb 2006
Posts: 55
#3

Re: Short Circuit Current

06/18/2009 4:47 AM

My dear friend calculate time per cycle either 60 or 50 cycles you have the answer for your question

crm

Reply
Commentator

Join Date: Nov 2008
Location: S.E. Asia
Posts: 91
Good Answers: 1
#4

Re: Short Circuit Current

06/18/2009 9:03 AM

Quote [Specifications says busbar to with stand 15KA for 1 sec however supplier is confirming 50KA for 1/2 cycle.]

This is the first time I've seen SC current specified in cycles. Are you sure this is not a typo? Normally, SC current is given in seconds so if it read "50kA for 0.5 secs", no problem but 50 kA for 10mS (1 cycle = 20mS@50Hz, 1 cycle = 16mS@60Hz)? Unheard of!!!

If it's 50kA for 0.5 secs, then your ok.

50² x 0.5 = 1250

__________________
"If you try to keep a leg each side of a barbed-wire fence, you'll do yourself a mischief." - Joh Bjelke-Petersen.
Reply
Reply to Forum Thread 4 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

elkangorito (1); JohnDG (1); murali (1); wareagle (1)

Previous in Forum: Multi-Core Clamp Meter   Next in Forum: Bus Bar Current

Advertisement