A transformer with 3-ph 415 V primary & 2-ph 24 V ac secondary. I am able to provide 2-ph 415 V ac supply to primary leaving 3rd ph unconnected. How much voltage will arise in 3rd ph left open and will this setup work without creating any problem ? Pls give proper solution since i have to apply this practically in my company.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Active Contributor

Join Date: Jun 2009
Posts: 21
#1

Re: Transformer

06/20/2009 4:20 PM

Is it a 480 vac step down transformer to 220 vac?

You will have taps on the secodary side where you will have 110 and 110 vac. these will give you 110 (120) on each phase to neutral( L1,L2,L3) and 220 (240) phase to phase ( L1, L2 ) Mostly used are higher voltages, now ( 277/480) less amps are used more efficiently. A delta transformer is needed for higher voltages But a Wye connction will give you more choices more amps used/required

Reply
Commentator

Join Date: Mar 2009
Location: Southern California
Posts: 97
Good Answers: 15
#2

Re: Transformer

06/21/2009 12:34 AM

If you have 415VAC 3ph delta, then the unconnected phase will have 415V to either of the other two phases. For voltage on a wye connection, divide by square root of 3.

If this is a high power transformer, leaving one phase unconnected could present a problem due to an unbalanced load. You might need to shift some other loads around so that each phase is supplying the same power. If it's smaller than, say, 3KVA then I wouldn't worry too much about load balancing. It's not the most efficient use of power but it's not going to blow anything up.

Reply
Member

Join Date: Apr 2008
Posts: 8
#3

Re: Transformer

06/22/2009 7:11 AM

Dear Guest!

Whenever the transformer is fully loaded, the primary winding willbe burnt out.

Please do not do such a mistake!

Peter

Reply
Guru

Join Date: Jul 2008
Location: SoCal USA
Posts: 556
Good Answers: 23
#4

Re: Transformer

06/22/2009 5:43 PM

Providing 2 phases out of 3 on the primary simply reduces the entire transformer to a 2 phase in/ 2 phase out. This will not present any problem electrically.

The voltage measured at the un-connected primary terminal represents the half-way point across 2 equal coils that parallel the actively energized coil and thus will voltage divide to about 1/2 of the 415v.

I am assuming that if the transformer was supplied with all 3 primary phases, there would be 3 secondary phases = 24 vac, though that was not the statement. Either way, only one 2phase output will be available at 24 volts. Due to internal connections, the other 2 secondary 2phase connections would measure in at around 12vac.

Regards, CJM

__________________
I do not 'know it all', but i will admit that I would like to. CJM
Reply
Commentator

Join Date: Nov 2008
Location: S.E. Asia
Posts: 91
Good Answers: 1
#5

Re: Transformer

06/24/2009 10:50 AM

There is no such thing as "A transformer with 3-ph 415 V primary & 2-ph 24 V ac secondary."

Anyway, this is obviously homework & anybody who provides detailed answers is not not helping this person.

__________________
"If you try to keep a leg each side of a barbed-wire fence, you'll do yourself a mischief." - Joh Bjelke-Petersen.
Reply
Anonymous Poster
#7
In reply to #5

Re: Transformer

06/25/2009 10:09 AM

Dear, There is such kind of thing since, i am using at my factory. Yet, i haven't faced any problem with the arrangement.

Reply
Commentator

Join Date: Nov 2008
Location: S.E. Asia
Posts: 91
Good Answers: 1
#8
In reply to #7

Re: Transformer

06/25/2009 11:52 AM

Well dear, I'll bet that it is not a "transformer"!! It may have a transformer in it...along with some electronics.

Again, there is no such thing as a transformer that can convert 3 phases to 2 phases. For example, the input of the transformer is 3 wire & the output of the transformer is 2 wire AND it does not contain any electronics.

__________________
"If you try to keep a leg each side of a barbed-wire fence, you'll do yourself a mischief." - Joh Bjelke-Petersen.
Reply
Guru

Join Date: Apr 2007
Location: Hyderabad, India
Posts: 596
Good Answers: 12
#6

Re: Transformer

06/24/2009 11:42 PM

Best example is 3 phase arc welding. If 1 ph is removed you get normal voltage but as you apply load then only voltage will drop. If current is low you can still use with just 2ph.

__________________
Subramanyam
Reply
Reply to Forum Thread 8 comments
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); CJMcGill (1); elkangorito (2); kvsubramanyam (1); Mitsurati (1); peterjohn (1); tonycaudill (1)

Previous in Forum: IEC 104 & 101.   Next in Forum: Good company for electronic soft starter.
You might be interested in: pH Electrodes, pH Transmitters, pH Instruments

Advertisement