Buried Power Cables and IEEE Standards

06/22/2009 11:20 AM

hello to one & all, i wanted to know that there should be a manhole provided or not for every change in direction of buried network of power cable as per iee standards?, if yes what is the code for it.please helpme, thankyou

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Jul 2007
Location: The cigarette-stained drunkard living in the cardboard box outside Marks & Sparks delivery entrance, Eastgate Shopping Centre, Basildon.
Posts: 487
#1

Re: power cable burried network

06/22/2009 11:43 AM

Code? It's common sense. How are you going to get a push-rod with a cable attached to its skinny end to turn left? <Splutter>

__________________
Essex jobs for Essex yobs! <Burp>.
Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#2
In reply to #1

Re: power cable burried network

06/22/2009 7:08 PM

I assume that the cable is installed in conduit. You need to install manholes after making pulling calculations for the cable. You are limited in the distance you can pull cable.

Register to Reply
Participant

Join Date: Apr 2009
Posts: 4
#3

Re: Buried Power Cables and IEEE Standards

06/23/2009 12:49 AM

The use of "standards" is to advise of the technical aspects that you will experience. The "most" important is that you will have a serviceable product that you have installed. There are some simple calculations on line about "Finding the amount of friction experienced for the X meter of cable. (assume it is in conduit that attaches both manholes) are listed many places on the net. They will tell you what the coeffinct of friction is that is influenced by the size of the cable, type of cable covering, the amount of pulling pressure that the end walls of the manhole and withstand before collapse and fail.

one of the other issues is that you site your manholes so that the cables enter and exit on the side ends of the manholes (a subsidiary, rather than a Lateral) this will also lower the friction requirements as well as the generous use of the correct cable pulling lubricant.

Enjoy

Elrod