Contaminated Refrigerant 134A

06/23/2009 5:37 PM

Hi to all,

We have two identical 5,000 tons chillers (1 and 2) that are in operation during the last few years, a contamination was noted in chiller 1 refrigerant as follows: 1) the isocarbon seal (shaft seal) were ruptured (replaced 2 times) 2) sight glass is being attacked by contaminated refrigerant (found scratches on glass or similar to sandblasted metal).

Appreciate it very much if anyone can find solution to resolve the above problem.

Cheers,

Rudy Fernando

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Commentator
India - Member - New Member

Join Date: Aug 2008
Posts: 61
Good Answers: 1
#1

Re: Contaminated Refrigerant 134A

06/24/2009 11:39 PM

Seal failure happen due to so many reason but, as you said you have found scratches on Sight glass similar to sand blasting on metals.

It seems, during Refrigerant charging if proper care is not done in that case something like sand etc. may enter in the system that might causing the Seal failure and scratches on sight glass.

I hope, the compressor is lubricated type & mech seal flushing by the same oil and so, check oil first ?

Did you took Oil sample and checked it ??

Do you have Compressor suction strainer with PDI ? Did you checked it when you replaced Mech. seal. ??

with regards,

Nilesh.

Register to Reply
Associate

Join Date: May 2007
Posts: 45
#2

Re: Contaminated Refrigerant 134A

06/25/2009 1:58 AM

You should take this up with the refrigerant manufacturer, get samples of refrigerant analysed as there appears to be a chemical reaction which is attacking the glass of the sight glass. R 134a is a mixture of several chemicals which have different boiling points. If you have a leak, it is possible that you will loose the highest boiling point chemical first, leaving a slurry of the low BP chemical. There could be a problem there which we are not familliar with. Please keep us informed of the test results.

Hope this helps

Phil

Register to Reply
Guru

Join Date: Aug 2005
Location: Hemel Hempstead, UK
Posts: 5826
Good Answers: 322
#3
In reply to #2

Re: Contaminated Refrigerant 134A

06/25/2009 2:38 AM

I know absolutely nothing about this sort of thing, but, if the composition of the refrigerant has changed significantly then surely it's performance will also have changed:-

rudy_fernando5r Apart from the damage: has the performance of the chiller changed in any way? Just monitoring the power consumed by both machines in similar circumstances may reveal a difference.

__________________
If you spend all your time looking for people and things to complain about: trust me, you will find plenty to complain about.
Register to Reply
Associate

Join Date: Dec 2005
Location: South Central Wisconsin
Posts: 35
Good Answers: 3
#4

Re: Contaminated Refrigerant 134A

06/25/2009 8:32 AM

You say Chillers are identical, but are operating and environmental condition identical?

R134a when exposed to excessive temperatures can break-down and form HYDROFLOURIC ACID and possibly CARBONYL FLOURIDE (per DuPont M.S.D.S. dated 08/24/95, page 5, Decomposition).

__________________
That which is watched, is optimized.........
Register to Reply
Active Contributor

Join Date: May 2009
Location: Philippines
Posts: 23
#10
In reply to #4

Re: Contaminated Refrigerant 134A

06/26/2009 3:00 PM

Thanks for your response.

Re operating and environmental conditions, both machines are located at the same plant room (air conditioned room). They are installed about 20 meters apart.

Cheers,

Rudy C. Fernando

Register to Reply
3
Anonymous Poster
#5

Re: Contaminated Refrigerant 134A

06/25/2009 9:19 AM

134a will hydrolyze at high temperatures and in the presence of high moisture to form hydrogen fluoride. Hydrogen fluoride readily etches glass and corrodes metals, particularly in the presence of moisture.

This can be confirmed by sampling the refrigerant and analyzing for acidity via aqueous conductivity. Acidity should be less than 100 ppb as HCl. (Be careful to avoid exposure to HF....it can be very corrosive to skin.) Refrigeration equipment suppliers can often provide this analysis.

High moisture can come from air in-leakage, which would also cause higher than normal refrigerant losses via the purge unit. In some cases it might also result from a tube leak in the condenser depending on shell / tube pressures.

High temperatures may result from compressor problems or problems with the oil still thermostat. Oil still thermostat problems will turn your oil dark.

Oil compatibility could also be a problem. If you don't use the right kind of oil, you can have acidity problems.

A short term fix is to swap out the entire refrigerant charge. But more than likely, the acidity will have permeated metal surfaces and the refrigerant side of the system will need to be cleaned.

Register to Reply Good Answer (Score 3)
Guru

Join Date: Jul 2008
Location: Anywhere I may be at the time
Posts: 661
Good Answers: 16
#6
In reply to #5

Re: Contaminated Refrigerant 134A

06/25/2009 11:06 AM

Sounds like you've "been there and done that" a couple times GA

Register to Reply
Power-User

Join Date: Jan 2007
Location: Houston,Texas
Posts: 378
Good Answers: 24
#7

Re: Contaminated Refrigerant 134A

06/25/2009 11:46 AM

Question 1: Why are you using R 134a for a 5000T unit? There are much more energy efficient refrigerants for use in large systems like yours. R-134a requires an extremely DRY system and meticulous attention to avoid any hot surfaces anywhere to avoid serious decomposition--which produces HF and other aggressive acids.

HF will etch glass surfaces like the sight glass. Immediately have the acid and moisture levels in the system checked. If wet, change the drier and keep changing it until the system is completely dry. If wet, the system is probably very acidic, which drastically accelerates 134a decomposition--as well as attacking all the metal and elastomers in the entire system. MAJOR damage will certainly result if left uncorrected.

Excess acidity CAN be removed/neutralized with the appropriate chemical treatment, but this is a job for Professional large scale refrigeration EXPERTS. The synthetic olube oil will also have to be drained and replaced. Contact the system manufacture and ask for assistance. The high acid level may be attacking the shaft seal components.

__________________
Keith E Bowers, PMP
Register to Reply
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#8

Re: Contaminated Refrigerant 134A

06/25/2009 4:52 PM

There is also the possibility that there has been some pump casting fragmentation. That is causing the problems. Any filter on the system?

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Register to Reply
Active Contributor

Join Date: May 2009
Location: Philippines
Posts: 23
#9
In reply to #8

Re: Contaminated Refrigerant 134A

06/26/2009 2:08 AM

Thanks for your response and other responses received.

After a few months operation of chiller no. 1 , the refrigerant could not be clearly seen from the sight glass, filters were installed to get rid of possible moisture/ contamination.

Both units (chillers 1 and 2) are in good operating conditions except the contamination noted in unit 1.

Cheers,

Rudy C. Fernando

Register to Reply
Register to Reply 10 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); Keith E Bowers (1); MrM (1); Nilesh (1); ozzb (1); philiplyon (1); Randall (1); rudy_fernando5r (2); Tim in Mexico (1)