Starting a 250HP Centrifual Blower

06/25/2009 8:35 PM

Hi all electrical experts,

I hv a 250HP centrifugal blower with close loop star / delta starter plan to connect to 500Kva DG,(only blower no other load) so can i start the said blower with traditional starter or need soft starter or VFD ? Please advise..

thank you

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Apr 2007
Posts: 577
Good Answers: 10
#1

Re: Starting of 250HP blower from 500Kva DG

06/25/2009 10:21 PM

Let do some simple calculation..

A 250HP Motor = 250HP x 0.746 KW = 186.5KW

Total running current = P/(V x I x 1.732 x 0.85)

Current (I) = 186.5KW/ (415 x 1.732 x 0.85) = 305.28 Amps

Diesel Generator = 500Kva

Total Current at 100% efficiency = Kva /(V x I x 1.732)

Current at 100% efficiency (I) = 500Kva / (415 x 1.732)

Current = 695.62 Amps

Assuming the Diesel Generator is about 95% efficiency after some electrical and mechanical losses, therefore the maximum power capacity that you have is about 660.84 Amps

Now, for starting your 250 centrifugal blower motor, with Star Delta starter, the starting current will be 1/3 of the DOL Starter. Therefore, your staring current will be,

Star-Delta Starting Amps= (305.28 x 7.5)/3 =763.2 Amps (13.4 % over your Diesel Generator output).

The above simple calculation shows that you will trip the MCCB of the Diesel Generator Panel during starting your 250HP centrifugal blower motor.

Other starter like soft starter, you got to know which type of the soft starter to buy. Most of the soft starter is a current limit starter where it required about 2.5 time of the FLC motor current. That mean, the soft starter will start your 250HP motor with 763.2 Amp.

There are some new soft starter, that start the motor with zero amps and slowly ramps up to the motor Full Load Current.

For me, I would prefer to go for VFD.

Now my question is,

Is your centrifugal blower is direct couple to the 250HP motor or it is a belt driven by pulleys. If it is a belts driven by pulleys we need to have your pulleys ratio (the Dimension) couple to the motor and the centrifugal fan.

The starting amps will be slightly different.

__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....
Reply Score 1 for Good Answer
Power-User

Join Date: Jun 2009
Posts: 223
Good Answers: 15
#2
In reply to #1

Re: Starting of 250HP blower from 500Kva DG

06/25/2009 11:48 PM

ok. yes. a soft starter that gradually ramps up the current from zero to flc is good thinking. a vfd is better still.

but when we are talking about a blower the spoiler is that the start will be heavy and the heaviness will prevail for relatively longer duration.

ordinarily - the switchgear trip settings and vfd/ss settings will take care of the same - the overload trip devices can even be temprarily bypassed for a short duration - BUT i have reservations about the generator performance for such a start - suggest that the start conditions as foreseeable should be shared with the generator manufacturer before pressing it into use.

Reply
Anonymous Poster
#6
In reply to #1

Re: Starting of 250HP blower from 500Kva DG

06/29/2009 8:37 PM

Thank you very much

Reply
Commentator

Join Date: May 2009
Location: Centurion, South Africa
Posts: 87
Good Answers: 5
#3

Re: Starting of 250HP blower from 500Kva DG

06/26/2009 3:49 AM

The problem with soft starter you are loosing torque on the motor during start up and the motor may not overcome the inertia of the fan impeller. This will eventually result in a trip.

VFD is the best option, because you get full motor torque at 1.5 times motor current (this current changes from different types of VFD's). The VFD should have no problem to accelerate the fan impeller.

__________________
R T F M .......
Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#4

Re: Starting of 250HP blower from 500Kva DG

06/26/2009 11:49 AM

DGs all have what is called "reserve capacity" for strarting motors, which is much larger than the FLA capacity. You cannot answer this question definitively without knowing the reserve capacity of the DG.

That said, there is a 'rule of thumb" that works MOST of the time.

For DOL (Across-the-Line) starting, the DG kVA must be at least 3X the HP (no conversion) or 4X the kW. So if you have a 250HP motor, you will need a 750kVA DG to start the motor DOL.

For a Solid State Soft Starter, the kVA must be 1.5-2X the HP or 3X the kW, so in your case that 500kVA should be fine. By the way, you CANNOT start a motor with FLA using a soft starter. I know that many brands allow you to adjust the Current Limit down that low, but an AC motor will not accelerate with that.

For VFD starting, you can use 1X the DG size. A VFD can start the motor with FLA in most cases.

I never use Y-Delta for starting large motors, in most cases it is a misconception that it reduces starting current and it has the potential to make matters a lot worse, both mechanically and electrically.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply
Guru

Join Date: Apr 2007
Posts: 577
Good Answers: 10
#5
In reply to #4

Re: Starting of 250HP blower from 500Kva DG

06/26/2009 8:13 PM

It is true.. Starting big motor with Y-Delta has the potential to make matters a lot worse, both mechanically and electrically because there is two in rush current for this Y-Delta starter. In other words, the motor will induce two in rush torque, that is during the star point and during the changer over point to delta. Normally, you will not see the damages but for long run, there will problem to the motor and the fan.

__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....
Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#7
In reply to #5

Re: Starting of 250HP blower from 500Kva DG

06/30/2009 12:28 AM

When I was a child, a local bully used to offer me a choice: one big hit with his closed fist or 2 slaps with his open hand. Neither was an attractive choice.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply
Reply to Forum Thread 7 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Aldego (1); Anonymous Poster (1); JRaef (2); Simon Wan (2); soebfatehi (1)

Previous in Forum: Distance Relays   Next in Forum: Reactive Power and Load or Line Impedance

Advertisement