Venting a Foam Insulated Roof

06/29/2009 11:57 AM

I am trying to determine the best way to install 4x8 sheets of 2.5 inch rigid foam board insulation (yellow foam sandwiched between black fiberglass roofing felt) in a cathedral ceiling.

I would like to keep the overall thickness of the roof as thin as possible and cut and install two layers of foam board between the 2x6 rafters. This would eliminate all but a half inch of air space under the 1/2 inch plywood decking which is covered with conventional three tab shingles.

Other options are placing one layer between the rafters and one layer below the rafters leaving 3 inches of air space or both layers below the rafters leaving 5.5 inches of air space. These options would require framing below the insulation to support the drywall which could be insulated as well with fiberglass batts but would lower the ceiling and require more materials and labor.

I would like to discuss what options there are for using the rigid foam board in the roof and the the placement of vapor retarder and ventilation to achieve the best insulating solution with the goal of keeping the roof system as thin as possible to maintain ceiling height.

We have hot, humid summers and moderate winters in western Ky.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#1

Re: To vent, or not to vent foam insulated roof?

06/29/2009 12:42 PM

Sounds like a lot of work! Retrofit is always more difficult. It would have been much simpler to attach the insulation and then the ½" plywood to the rafters. But hindsight is 20-20.

One very important consideration could be the shingle manufacturer. Many of them won't give a warranty unless an attic space is properly ventilated. Trapped air (with leaks) becomes a one way moisture pump. You will occasionally see this effect in automobile taillights sloshing a few ounces of water in one (and not the other). You want to avoid that situation.

Another consideration is whether the shingle nails are penetrating through the ½ plywood. If not now, then what happens when the next roof is applied? Also consider that you will have a small gap between the insulation and the rafter unless you install a mounting strip like a 2x2 on both sides of the rafter. At least that way you would have a flat surface for the insulation board to seal to a mounting strip. But the air gap between the insulation and the under side of the plywood would need an opening at the eave and a ridge vent the entire length of the roof to prevent a condensation buildup. At least that way you could install two solid layers (overlapping the joints so that one is not in line with the other). And you will probably use a few cases of caulk, between the edges of the insulation and the rafter, for both layers.

Look for an architect to get a better opinion, but don't neglect the shingle mfg. requirements.

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Register to Reply
Power-User

Join Date: Jun 2008
Location: Kentucky Lake
Posts: 390
Good Answers: 26
#2
In reply to #1

Re: To vent, or not to vent foam insulated roof?

06/29/2009 1:46 PM

Thanks for the response, Joe.

I don't know if this is retrofit, remodel or "new construction". The roofing is 23 years old and will probably be replaced in the next few years, possibly with metal, but the house has never been insulated or drywalled. (If I knew how to post a picture I would and that might help.) The nails do penetrate the plywood so it would punch into the foam which is not a problem unless I need a vapor barrier under the decking (one contractor suggested plastic between the deck and the foam but it would get a bunch of holes punched in it).

If I put the foam board against the decking using cans of expanding foam I was hoping to eliminate any trapped air and I was planning on using the expanding foam to fill any gaps and adhere the foam to the rafters. I found a reference to a study that said foam insulation sprayed directly on the decking between the rafters does not make the shingles hotter than a conventional vented roof, but I could not find the original research report.

Good tip on the shingle mfgs. Thanks again.

Register to Reply
Power-User

Join Date: May 2009
Location: Upstate NY USA
Posts: 148
Good Answers: 7
#3

Re: Venting a Foam Insulated Roof

06/29/2009 7:10 PM

The most important thing is to ventilate the roof. The roof deck should always be as close to the outside air temperature as possible.

The best suggestion I can give is to install a ridge vent the entire length of the roof:

http://www.lowes.com/lowes/lkn?action=howTo&p=Improve/ridgevent.html

With the roof deck isolated from the space below, you will need to install soffit vents between all the rafters- continuous soffit vents would be the best way to do this:

http://www.tamlyn.com/index_files/ezvent.htm

This will allow air to flow naturally under the roof deck, keeping it cool in summer and in winter (which prevents ice dams).

Keeping the roof cool and well-insulated from the house will save you money on your air conditioning also. I would suggest a vapor barrier between the rafters and the sheetrock to keep your warm or cool air in.

Just a question- why did you pick rigid foam and not fiberglass? More R-value for a given thickness, I assume?

__________________
ASCII silly question, get a stupid ANSI.
Register to Reply
Power-User

Join Date: Jun 2008
Location: Kentucky Lake
Posts: 390
Good Answers: 26
#5
In reply to #3

Re: Venting a Foam Insulated Roof

06/30/2009 7:59 PM

I'm trying to keep the ceilings as high as possible, particularly over a staircase and I will have triangle windows in the gable ends, which I would like to be as large as possible. I found the foam sheets for seven dollars each, so I bought 100 of them. Enough to do two layers on a 15 square roof.

I have seen manufactured sheets of foam and plywood laminated together and the top layer has 3/4 inch airspace under it. That seems like very little ventilation. I can do ridge and soffit vents, but what do you think the minimum space under the deck could be for a rafter about 12 feet long.

Register to Reply
Power-User

Join Date: May 2009
Location: Upstate NY USA
Posts: 148
Good Answers: 7
#9
In reply to #5

Re: Venting a Foam Insulated Roof

07/03/2009 12:56 AM

If it were my roof, I would nail 1x2s (or strips of wood/plywood ripped to size) along the rafters (making them thicker) and then use both layers of foam panel like you originally planned on. That will give you an inch or so of air space, and only cost you 1/2" or 3/4" of ceiling height. A plastic vapor barrier between the insulation panels and the sheetrock would be a good idea also.

__________________
ASCII silly question, get a stupid ANSI.
Register to Reply
Power-User

Join Date: Jun 2008
Location: Kentucky Lake
Posts: 390
Good Answers: 26
#10
In reply to #9

Re: Venting a Foam Insulated Roof

07/04/2009 11:51 AM

This is a good idea to add to the bottom of the rafters. I could even rip 2x4s in half. The way things are built now, I could easily drop the ceiling a few inches without too much trouble. Thanks! A local builder/neighbor suggested putting the plastic on top. Does the location of the vapor barrier vary by geographic location.

Register to Reply
Guru
Popular Science - Weaponology - bwire Hobbies - Car Customizing - New Member

Join Date: Dec 2007
Location: Upper Mid-west USA
Posts: 7498
Good Answers: 97
#11
In reply to #10

Re: Venting a Foam Insulated Roof

07/05/2009 4:35 AM

Don't use a vapor barrier on ceilings, the gap from eave to peak between sheathing and insulation materials is the means to vacate vapor.

__________________
If death came with a warning there would be a whole lot less of it.
Register to Reply
Active Contributor

Join Date: Apr 2009
Location: Nokomis IL
Posts: 18
#4

Re: Venting a Foam Insulated Roof

06/30/2009 11:52 AM

There is a 'closed cell' spray foam, made from soybeans, that expands. CPI also sells spray on roofing. Might be an option.

Register to Reply Score 1 for Good Answer
Power-User

Join Date: Jan 2008
Location: Toronto, Canada
Posts: 302
Good Answers: 4
#6
In reply to #4

Re: Venting a Foam Insulated Roof

07/01/2009 11:10 AM

I was going to suggest the same thing.

It's like the expanding foam insulation you can buy in hardware store for sealing cracks in wall. They have different formula for different purpose. You may need to call someone to spray it.

__________________
Pineapple
Register to Reply
Power-User

Join Date: Jun 2008
Location: Kentucky Lake
Posts: 390
Good Answers: 26
#7
In reply to #6

Re: Venting a Foam Insulated Roof

07/01/2009 12:25 PM

I'm aware of the spray on foam and it is an excellent product. They spray this directly to the bottom of the sheathing on the roof between the rafters and it works well for cathedral ceilings. They can do this without any ventilation (as I understand it) because it is not air/moisture permeable. I already have 3200 square feet of 2.5 inch thick foam boards I would like to put directly on the bottom of the roof sheathing in a similar way using the cans of foam if possible. I just can't find much info on insulating this way and the long term results.

Register to Reply
Guru
Popular Science - Weaponology - bwire Hobbies - Car Customizing - New Member

Join Date: Dec 2007
Location: Upper Mid-west USA
Posts: 7498
Good Answers: 97
#8
In reply to #7

Re: Venting a Foam Insulated Roof

07/01/2009 1:14 PM

Look at this from Cor-A-Vent, it is designed for use under siding but I can see no reason the design wouldn't be applicable in your use too.

Of course anything such as furring strips, lattice, half or quarter rounds glued to the underside of sheathing would work too.

I have a similar situation which I'm thinking to use a corrugated material as spacing.

__________________
If death came with a warning there would be a whole lot less of it.
Register to Reply
Participant

Join Date: Jul 2010
Posts: 1
#13
In reply to #8

Re: Venting a Foam Insulated Roof

07/23/2010 10:27 AM

Can you post that Cor-A-Vent link again? Whatever's behind the word "this" isn't working.

Same problem here -- 8" rafters, house in the Virginia mountains built in the 1960s, half cathedral roof.

I'm trying to set this up from 3000 miles away. The last roofer cheated my 90-year-old mom a decade ago, put on shingles with half the nails required, overdriven. Nails punched through the shingles, which are now sliding off.

Gotta decide early next week what to do.

Deck of half inch plywood maybe delaminating from water.

Local roofers aren't into new technology -- no foam-core-metal standing seam panels, common in California where I live. No sprayon foam roofs that could go over what's there. Local architect has energy efficiency ideas, but all novelties, likely to get very expensive because they'd be brand new (like put down a new deck, then rigid foam, then metal roof ... builder/roofer are just "huh??").

In the Virginia mountains, I can get:

-- add new shingles over the old, maybe, or rip off the deck and reshingle

OR

-- put rigid foam dropped into the 8" rafter space over the cathedral ceiling half of the house, add a peak vent, put down new deck, and shingles.

I might get them to put aerogel on top of the rafters before attaching new deck -- said to cut thermal bridging by 15 percent. It's self-sticking, nail/screw right through it: http://www.thermablok.com. Not familiar but not too complicated or scary to add, maybe.

But --- same question how much air space over rigid foam in an 8" rafter space?

What's the best _available_ practice for making this 45-year-old roof more energy-efficient?

I can get a friend-of-a-friend local contractor to supervise. But he wants direction about what to do.

Heck, I'm going to have a hard time getting white or cool-roof shingles. Nobody has a white roof ....

Register to Reply
Participant

Join Date: Jan 2010
Location: Huntsville, Alabama
Posts: 1
#12

Re: Venting a Foam Insulated Roof

01/08/2010 4:26 PM

I have read on buildingscience.com about good design practices. Namely for the warm mixed climate in Kentucky (like mine in northern Alabama) there is a need to allow the roof assembly to "dry to the inside" when the exterior vapor pressure (from a rain and then heat) drives vapor moisture through the shingles and roofing felt. Any vapor barrier, either the roof-sheathing-mounted-insulation itself or a barrier on the interior side of the insualtion, will trap the vapor and create a mold concern (again this is specific to a warm-mixed climate, it's different for hot-humid, cold-mixed, etc).

A vapor "retarder" is fine, a vapor "barrier" on the interior of a roof seems to be a concern in warm-mixed. A couple inches of closed-cell foam is a retarder (i.e. the vapor has to work to get through but it can), much more than that and the "retarder" becomes a "barrier" and the vapor is trapped. Open cell foam allows the vapor to go in and out realtively freely, but open cell has ~ R-4/inch rather than closed cell ~ R-7/inch.

Personally, for my retro-fit that I'm currently executing, I installed 4" thick foil faced polyiso foamboards under my rafters, left about a 1" gap between adjacent boards for me to fill/seal with open cell foam (this allows the vapor/moisture to exit), and blew densely packed cellulose insulation above the foamboard and below the roof sheathing. The majority of the acreage then has foil-faced 4" poliso (~R28 and vapor impermeable and air impermeable) and 5.5" cellulose (~R19 air and vapor permeable) for an ~R47 air impermeable and vapor impermeable solution in 9.5". Gaps to allow the vapor to escape still have the 5.5" cellulose and 4" of open cell spray foam for an ~R33 air/vapor "permeable" solution that allows the vapor to escape.

Register to Reply
Register to Reply 13 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!