Transformer Surge Arrestor

07/02/2009 9:18 PM

Good days all Gurus,

In my manufacturer palnt,I have noticed some 6.6KV / 200 to 400v 3 phase tap changing transformer (1200Kva) has installed with surge arrestor at the input terminal But some 22KV / 6600v 3 phase transformer (3500kva)didnt installed with surge arrestor.

Please advise me the reason of of installtion of surge arrestor ?

Thank you very much

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster
#1

Re: Transformer Surge Arrestor

07/04/2009 1:15 AM

Hi Aikhh,

The reason why the surge arrestors installed are used to protect transformers against overvoltages, which is important part of the power system.

Overvoltages sometime occurs during switching over operations of nearby circuit breakers or as a result of lightning strokes.

Kind regards

Roman

Register to Reply
Power-User

Join Date: Jun 2006
Location: Manila Philippines
Posts: 171
Good Answers: 8
#2
In reply to #1

Re: Transformer Surge Arrestor

07/04/2009 1:20 AM

Sorry, It seems I was not logged in when I replied in this post.

Register to Reply
Anonymous Poster
#3
In reply to #1

Re: Transformer Surge Arrestor

07/04/2009 10:41 PM

I appreciate if it can be briefed regarding the application of surge arrestors,their location and their types.Recently we had come across sudden surge in the distribution voltage upto 260 volts due to which failure of some of the tube lights,exhaust fans etc. had been experienced.The transformer input voltage is 11kv which is steppeddown to 440 volts and futher distributed to various motors at 230 volts.Pl. advise how to avoid such type of failures.

Register to Reply
2
Power-User

Join Date: Jun 2006
Location: Manila Philippines
Posts: 171
Good Answers: 8
#5
In reply to #3

Re: Transformer Surge Arrestor

07/06/2009 1:18 AM

Dear Guest,

Hope this info would help and meet your question on this post.

Introduction

Damage from electrical transients, or surges, is one of the leading causes of electrical equipment failure. An electrical transient is a short duration, high-energy impulse that is imparted on the normal electrical power system whenever there is a sudden change in the electrical circuit. They can originate from a variety of sources, both internal and external to a facility.

Not Just Lightning

The most obvious source is from lightning, but surges can also come from normal utility switching operations, or unintentional grounding of electrical conductors (such as when an overhead power line falls to the ground). Surges may even come from within a building or facility from such things as fax machines, copiers, air conditioners, elevators, motors/pumps, or arc welders, to name a few. In each case, the normal electric circuit is suddenly exposed to a large dose of energy that can adversely affect the equipment being supplied power.

The following is a guideline on how to protect electrical equipment from the devastating effects of high-energy surges. Surge protection that is properly sized and installed is highly successful in preventing equipment damage, especially for sensitive electronic equipment found in most equipment today.

Grounding Is Fundamental

A surge protection device (SPD), also known as a transient voltage surge suppressor (TVSS), is designed to divert high-current surges to ground and bypass your equipment, thereby limiting the voltage that is impressed on the equipment. For this reason, it is critical that your facility have a good, low-resistance grounding system, with a single ground reference point to which the grounds of all building systems are connected. Without a proper grounding system, there is no way to protect against surges. Consult with a licensed electrician to ensure that your electrical distribution system is grounded in accordance with the National Electric Code (NFPA 70).

Zones Of Protection

The best means of protecting your electrical equipment from high-energy electrical surges is to install SPDs strategically throughout your facility. Considering that surges can originate from both internal and external sources, SPDs should be installed to provide maximum protection regardless of the source location. For this reason, a "Zone of Protection" approach is generally employed. The first level of defense is achieved by installing an SPD on the main service entrance equipment (i.e., where the utility power comes into the facility). This will provide protection against high energy surges coming in from the outside, such as lightning or utility transients.

However, the SPD installed at the service entrance will not protect against internally generated surges. In addition, not all of the energy from outside surges is dissipated to ground by the service entrance device. For this reason, SPDs should be installed on all distribution panels within a facility that supply power to critical equipment. Similarly, a third zone of protection would be achieved by installing SPDs locally for each piece of equipment being protected, such as computers or computer controlled devices. Each zone of protection adds to the overall protection of the facility as each helps to further reduce the voltage exposed to the protected equipment.

Coordination of SPDs

The service entrance SPD provides the first line of defense against electrical transients for a facility by diverting high-energy, outside surges to ground. It also lowers the energy level of the surge entering the facility to a level that can be handled by downstream devices closer to the load. Therefore, proper coordination of SPDs is required to avoid damaging SPDs installed on distribution panels or locally at vulnerable equipment. If coordination is not achieved, excess energy from propagating surges can cause damage to Zone 2 and Zone 3 SPDs and destroy the equipment that you are trying to protect.

SPD Ratings

When selecting an SPD for a given application, there are several considerations that must be made:

  • Application - Ensure that the SPD is designed for the zone of protection for which it will be used. For example, an SPD at the service entrance should be designed to handle the larger surges that result from lightning or utility switching.
  • System voltage and configuration - SPDs are designed for specific voltage levels and circuit configurations. For example, your service entrance equipment may be supplied three phase power at 480/277 V in a four-wire wye connection, but a local computer is installed to a single-phase, 120 V supply.
  • Let-through voltage - This is the voltage that the SPD will allow the protected equipment to be exposed to. However, the potential damage to equipment is dependent on how long the equipment is exposed to this let-through voltage in relation to the equipment design. In other words, equipment is generally designed to withstand a high voltage for a very short period of time, and lower voltage surges for a longer period of time. The Federal Information Processing Standards (FIPS) publication "Guideline on Electrical Power for Automatic Data Processing Installations" (FIPS Pub. DU294) provides details on the relationship between clamping voltage, system voltage, and surge duration.

    As an example, a transient on a 480 V line that lasts for 20 microseconds can rise to almost 3400V without damaging equipment designed to this guideline. But a surge around 2300 V could be sustained for 100 microseconds without causing damage. Generally speaking, the lower the clamp voltage, the better the protection.

    Surge current - SPDs are rated to safely divert a given amount of surge current without failing. This rating ranges from a few thousand amps up to 400 kiloamperes (kA) or more. However, the average current of a lightning strike is only approximately 20 kA., with the highest measured currents being just over 200 kA. Lightning that strikes a power line will travel in both directions, so only half the current travels toward your facility. Along the way, some of the current may dissipate to ground through utility equipment.

    Therefore, the potential current at the service entrance from an average lightning strike is somewhere around 10 kA. In addition, certain areas of the country are more prone to lightning strikes than others. All of these factors must be considered when deciding what size SPD is appropriate for your application.

    However, it is important to consider that an SPD rated at 20 kA may be sufficient to protect against the average lightning strike and most internally generated surges once, but an SPD that is rated 100 kA will be able to handle additional surges without having to replace the arrester or fuses.

    Standards - All SPDs should be tested in accordance with ANSI/IEEE C62.41 and be listed to UL 1449 (2nd Edition) for safety.

Data Line Protection

Electrical transients are not confined to the electrical distribution system. They can enter a facility through phone/fax lines, cable or satellite systems, and local area networks (LAN). Therefore, in order to achieve maximum protection from surge damage, SPDs should be installed on all systems susceptible to electrical transients.

Installation

For maximum protection, SPDs should be installed as close to the equipment being protected as possible. Cable lengths should be as short and straight as possible to minimize the resistive path of the circuit to ground. A solid connection to the system grounding conductor is essential for proper operation of the SPDs. The surge protectors should be equipped with indicators that show if the circuit is grounded and operating properly, and the units installed so these indicators can be easily inspected.

All service entrance and distribution panel SPDs should only be installed by a licensed electrician familiar with the equipment and its use. In addition, Hartford Steam Boiler strongly recommends that a professional engineer experienced with surge suppression technology be retained to design the protection scheme for your facility to ensure all SPDs are properly sized and coordinated.

Kind regards

Roman

Register to Reply Good Answer (Score 2)
Guru
Popular Science - Biology - life lover Hobbies - Musician - music lover Safety - Hazmat - better safe than sorry United Arab Emirates - Member - desert trek Technical Fields - Procurement - procurement

Join Date: Sep 2008
Location: Dubai, UAE
Posts: 744
Good Answers: 58
#4

Re: Transformer Surge Arrestor

07/05/2009 5:01 AM

first of all, aikhh, the Gurus themselves will appreciate it if you would not address your question only to them. this forum has a wealth of minds, and most of them are not yet gurus. you will only alienate those who are willing to help, but are not gurus.

__________________
Now the darkness only stays the night-time, in the morning it will fade away. -- George Harrison (All Things Must Pass)
Register to Reply Off Topic (Score 5)
Active Contributor

Join Date: Apr 2007
Location: South Africa - Vaal Triangle
Posts: 10
Good Answers: 1
#6

Re: Transformer Surge Arrestor

07/06/2009 3:59 AM

Another reason why not all the transformers may not be installed with surge arrestors is because of the circuit breaker type (i.e. air or vacuum). Due to the switching transients associated with the vacuum circuit breakers (and contactors) it is recommended that the surge arrestors are installed at the load side (i.e. be it a transformer or a motor). This is because of the "early current chop", which is characteristic of the vacuum type interrupters. This "current chop" happens just before the first current zero crossing, which causes a high dI/dt and hence over-voltages at the load side. This therefore necessitates installation of a surge protective device (SPD) to protect the transformer or the motor.

NB:- Apart from the "current chop", other causes of surges associated with vacuum type interuptes are the"current re-ignition", "current pre-ignition" and "3-phase simultaneous interruption".

Hope that this helps.

Regards,

Eddy Mahlatsi

South Africa

__________________
Imagination has no limit...
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Mar 2009
Posts: 130
#7
In reply to #6

Re: Transformer Surge Arrestor

07/07/2009 2:44 AM

Hi EddyM,

Thank you very much of your very good answer,as for your information,my glass plants we have 5 units of 'booster transformer' which capacity from 750Kva to 1200Kva. All the surge arrestor is install at transfomer terminals ,primary (incoming 6600V 50Hz) after the VCB and all these transformer with 'tap changing' feature which is change the input tap to this transfomer and seconday ouput ( 3 group of indepent winding) and connect to load (molten glass at 1550deg c).

Regards

Register to Reply
Register to Reply 7 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

aikhh (1); Anonymous Poster (2); EddyM (1); langyaw (1); Roman (2)