hi ,i m sorry i did a mistake,the rated current is 124A & full load current is 18.60A, now which one should be considered for the load cal ,& breaker size sellection.
thank you every body
Re: breaker size
07/08/2009 3:51 AM
Re: breaker size
07/08/2009 5:34 AM
This information also wrong.
A motor rated at 124 A and full load is 18.6 A that mean the motor less than 15KW motor.
Please double check the amps again
Re: breaker size
07/08/2009 4:01 PM
This is elementary electrical protection theory every electrician knows. Please get a professional to do the design and installation for you before you kill yourself and/or others as you are clearly not qualified to perform this type of work.
If this is a homework question, this is not a homework cheat site.
Reply Score 1 for Off Topic
Re: breaker size
07/09/2009 7:15 AM
It's not the size of your breaker, it's how you use it.
Re: breaker size
07/09/2009 2:07 PM
Back in the dawn of time, I worked in an old mill that ran all 220v delta 3-phase. All the motors were fused for 10 amps / hp. I was told that this was for start-up current, but they would only draw 3 amps / hp at full load. This I confirmed by cleaning numerous data plates and reading them for run current. (Last patent dates on some of these motors was 1913.)
How can you be two places at once when you're actually nowhere at all?