Electrical Engineering

07/11/2009 2:10 AM

Can We run the 3phase Induction motor 30HP in star and delta both for different application in one machine,i.e. wire drawing machine of steel plant. the use of motor in inching mode in star and run mode in delta with help of two seperate contactor ML-06 & ML-4 (L&T Make).Presently we are operating the motor by only one contatcor ML-06 in DOL.

MK

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2007
Posts: 2550
Good Answers: 103
#1

Re: Electrical Engineering

07/11/2009 4:22 AM

Your question is not very clear.

Whether you run in star or delta, the speed of motor will be same ie synchronous*(1-slip). If you want to reduce the speed it goes into unstable region of slip-torque curve and stalls.

So there is no question of running in inching unless it is with a VFD or with the reducers.

As far as star is concerned, it is run either at start when the higher current will generate more torque or if it runs at the partial load (typically <50% of rating) in that case it improves the power factor as well as efficiency, but of course at the cost of the available power.

BTW: do not keep on switching it on and off in inching. Each time you switch on, the huge current passes through the motor, and is several times the rated current even in star. This is not healthy for the motor or for the insulation. Normal motors (unless specifically designed for inching) are only designed for a few times On/OFF in a given period. If you want then you have to get the specific motor, duly over rated that can handle this.

__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches
Reply Score 1 for Good Answer
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#2

Re: Electrical Engineering

07/17/2009 8:41 AM

I do not know what duty class of motor u are using. If it is s1 its not suitable.For inching u should use s4 or s5 as required Like in Cranes where frequent starts and stops takes place.

__________________
To avoid crticism do nothing,say nothing,be nothing
Reply
Reply to Forum Thread 2 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!

Previous in Forum: 1000-A Contactors   Next in Forum: Starter and deep cycle charging differences?

Advertisement