thermocouples

07/18/2009 1:11 PM

What is minimum distance between three thermocouples (2oo3) mounted on same pipe line (20")? Technically accepted by stright line mounted or circler mounted?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Commentator

Join Date: Apr 2009
Location: Texas
Posts: 57
Good Answers: 2
#1

Re: thermocouples

07/19/2009 7:53 AM

120 degrees in the same plane (circular), especially if there has not been sufficient thermal mixing of the process at the point of measurement. In this case, the average of the temps should be used for control (as opposed to the middle of 3) in addition to any deviation checking used to detect a failed TC.

If any thermal streaming is occurring, then mounting the TCs linearily down the pipeline reduces your chances of measuring it.

This approach may be overly cautious depending on your application, but this was a real world headache for me that I thought I'd share.

Register to Reply Score 1 for Good Answer
Power-User
Australia - Member - Igor...pull the switch!!!

Join Date: Apr 2009
Location: Australia, sunny North Queensland
Posts: 380
Good Answers: 12
#2
In reply to #1

Re: thermocouples

07/20/2009 9:56 AM

Agreed and complete answer

__________________
CraziestOzzy
Register to Reply
Register to Reply 2 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!

Previous in Forum: GAS Line Pressure Switches to Calibrate   Next in Forum: scan time DCS
You might be interested in: Distance Meters, Line-shaft Spools

Advertisement