No Load Motor Trial Procedure

12/10/2006 12:42 AM

dear engineers,

whats the procedure for motor no load trial run. Can we run the 250kw LT motor in no load condition for 4 hours (we has run the motor in no load for setting of motor bearings - some body telling its correct some body telling its wrong. whats ture we want to know)?

regards

hari

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Member

Join Date: Dec 2006
Posts: 8
#1

Re: No Load Motor Trial Procedure

12/11/2006 12:57 AM

Dear Sir,

No Load testing of Motor will be conducted only to know Magnetizing Current of the Motor.

To check the Motor performance like,Heating of body,Bearings,Power Consumption,Power factor Motor has to run on diffrent Loading Conditions staring from 25% to 125%.

During loading condition there should not be rise in temperature of Bearings and Motor body after attaining the saturation level.

Regards

Aruna Kumar

Register to Reply
Guru

Join Date: Jan 2006
Location: Tamworth, UK.
Posts: 1782
Good Answers: 45
#2

Re: No Load Motor Trial Procedure

12/11/2006 7:14 AM

You do not say what type of motor it is but in the old DC days 'series' wound motors were quite common. They were used because of their high torque slow speed characteristics.

It was (still is) dangerous to run these motors on no-load because with nothing to stop them (except bearing and commutator friction) (and residual magnetism of the field coils) they run faster and faster and faster - until (usually) the armature bursts (due to enormous centrifual force). The resultant siezure would instantly transfer the angular momentum to the frame which could rip the motor off it's feet to go rolling away to skittle everything in it's path.

It is an incident that tends not to pass unnoticed.

__________________
When arguing, remember mud-slinging = lost ground.
Register to Reply
Power-User
United States - Member - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: May 2006
Location: Pittsburgh PA
Posts: 121
#3

Re: No Load Motor Trial Procedure

12/11/2006 9:14 AM

Routine testing of Motors does include a No Load test

During which you will check Curent, Voltage, Power, Speed and Mechanical Vibration.

You want to find the NO-Load Loss

Standards are ANSI C50.41-2000

NEMA MG1-1998 Rev 1Section 20.16 and IEEE 112

Check latest revs of all.

You will want to load the motor

25%-150%

__________________
“There's a sucker born every minute, and I happen to be one of them”
Register to Reply