Generator Rotor Fault Detection

07/26/2009 7:22 AM

How can incipient rotor turn-to-turn winding faults be detected in a 16MW, 15kV, 3-phase 60Hz 1200 rpm synchronous generator with salient pole rotor, while generator is in operation?

Register to Reply
Pathfinder Tags: Generator Winding Faults
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#1

Re: Generator Rotor Fault Detection

07/27/2009 12:14 AM

Very quickly I would imagine (increased current, heat and failure). I wouldn't want to be any where near one if it developed a turn-to-turn fault while under load.

Why do you ask?

__________________
jack of all trades
Register to Reply
Active Contributor

Join Date: Jul 2008
Location: Mombasa, Kenya
Posts: 24
Good Answers: 1
#2

Re: Generator Rotor Fault Detection

07/27/2009 4:15 AM

If such a fault were to happen (on one pole), the electromagnetic field would be affected, creating an effective imbalance both in the mechanical and electrical components. If the AVR continous to support the increased current drawn to maintain the stator terminal voltage, then there will be increased vibration, pole-shoe temperatures and possible generator bearing failure as a consequence of the increased vibration.

I think the best way is to monitor the AVR current. Vibration analysis would give you an indication but requires that you have initial good values of the whole system to compare with. Really depends on how the AVR is set up to handle reactive power for the generator.

__________________
Curiosity has its reasons for existence - Albert Einstein
Register to Reply
Power-User
Hobbies - HAM Radio - New Member

Join Date: Oct 2008
Location: Houston, Texas
Posts: 252
Good Answers: 5
#3

Re: Generator Rotor Fault Detection

07/27/2009 11:08 AM

What about monitoring the excitation current, voltage and generator output MW to see if the relationship changes. As long as the resistance of the rotor winding does not change appreciably, the relationship should be fairly constant.

If there are turns shorting in the rotor, I would expect to see the excitation current increase and the excitation voltage drop while the MW out remains about the same or the excitation voltage drop and the excitation current remain about the same while the MW output decreases some.

I am sure I have seen an alarm for this as well as a rotor ground fault alarm on a control system I once worked on but don't really know how it was done.

__________________
If the software can detect, compensate, avoid, or correct an anomalous condition in the system, it is, by definition, a software problem-regardless of the root cause. In the long run, for most classes of problems, it is cheaper to fix it in the SW
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#4

Re: Generator Rotor Fault Detection

07/27/2009 11:13 AM

16MW is a lot of power. Since a turn to turn winding fault will likely be across adjacent turns of the same phase and thus be a shorting loop of a small part of an output loop, it maybe very difficult to detect. Complicating your search will be output load changes beyond your control. One possible idea would be to monitor the DC current applied to the rotor and compare this with the changes in the AC output current of all three phases. Fluctuations in the rotor current that don't correlate with output current load changes might implicate an insulation breakdown. Particularly if a higher rotor current correlates with the voltage of the one phase with a short in it. But this may just be an artifact of the high noise environment.

The thermal effect suggested by others of this short maybe your best bet.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Power-User
Hobbies - HAM Radio - New Member

Join Date: Oct 2008
Location: Houston, Texas
Posts: 252
Good Answers: 5
#5
In reply to #4

Re: Generator Rotor Fault Detection

07/27/2009 11:22 AM

I thought a fault in the rotor would affect all of the phases roughly equally since the rotor provides the excitation field for all of the windings in the stator.

Please correct me if I am wrong.

Thanks!

TT3

__________________
If the software can detect, compensate, avoid, or correct an anomalous condition in the system, it is, by definition, a software problem-regardless of the root cause. In the long run, for most classes of problems, it is cheaper to fix it in the SW
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#6
In reply to #5

Re: Generator Rotor Fault Detection

07/27/2009 12:23 PM

You caught me. I misread and thought the original question was about a short in one of the three stator windings. A short in the rotor winding would affect all three output phases. (Maybe somebody should mark my previous answer as off topic. ) A rotor short would make the generator less efficient, but measuring the applied power for delivered power at 16MW would be tricky at best. If the short is an intermittent you might be able to notice an output power dip that corrolates with rotor current spikes.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply