CT Connection

07/28/2009 8:32 AM

Hey.....If I reverse the current transformer (CT1) primary connection feeding from another CT2(P1 to S2(ct2) & P2 to S1(ct1)) instead of (P1 to S1(ct2) & P2 to S2(ct1) finally being connected to the ammeter will there be any problem in measurement.....???

__________________
"Know something about everything and everything about something"
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Mar 2007
Posts: 2550
Good Answers: 103
#1

Re: CT connetion

07/28/2009 10:07 AM

If I understand correctly then No.

The Line Current (I) is reduced to the ratio n1 ie the current at the secondary of CT1 is I/n1

Then as you connect it on the second transformer (n2) this line current (I/n1 ) is reduced to I/n1n2 on the secondary of the CT2

But this is only if you want to measure the current. If it is for any other measurement - remember the current is now 180o out of phase with the primary. And that will create havoc with power measurements.

__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches
Register to Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#2
In reply to #1

Re: CT connetion

07/28/2009 8:13 PM

I agree with guru sb.

This can be done for ammeter with having correct reading but it won't work for other meters (such as Watt meter, Energy meter, pf meter etc.) where the CT polarity is a concern.

-MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply
Active Contributor

Join Date: Jul 2009
Location: Western Australia
Posts: 24
#3

Re: CT Connection

07/29/2009 8:02 PM

If your two CT's are measuring the same phase for a multi generator cross-current-compensation circuit, then they will null each other out and the machines will not balance load properly in Isochronous mode.