UPS Bypass Transformer

08/06/2009 4:43 PM

What are the advantages and disadvantages for using the Ferroresonance Regulating Transformer and Shielded Isolation Transformer for the UPS Bypass system?

-MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Aug 2008
Location: West Virginia
Posts: 185
Good Answers: 12
#1

Re: UPS Bypass Transformer

08/07/2009 11:04 AM

A ferroresonant transformer runs with the core always in saturation which produces a very precise regulated output. Since it is saturated, the output will be a square wave. That works great for DC power generating circuits but generally is very undesirable for normal AC applications. Almost everything AC is designed for sign waves which are very expensive to produce from a square wave source. Most motors will not run on square waves. Most dimmers, etc won't either. It overheats most computer power supplies if they will work at all.It does however do a pretty good job of filtering most higher frequency noise coming from the input.

Faraday shielded transformers run as a normal transformer in all respects. The Faraday shield keeps high frequency noise (especially common mode) from coupling from the primary to the secondary. Most isolation transformers are Faraday shielded for this reason.

Bottom line is stay away from ferroresonant transformers if you're not sure.