Energy Meter (KWH Calculation)

08/11/2009 11:31 AM

Hi,

I am using an energy meter in Generator.

Now that energy meter is not showing accurate Energy Generated it is getting PT Voltage in all 3-Phase (110V) But CT Current is Missing in 1 phase.

Meter has only two phase CT Input.

Now is there any formulae by which I can calculate the accurate energy reading from the Value which meter is showing?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Guru

Join Date: Jul 2008
Location: SoCal USA
Posts: 556
Good Answers: 23
#1

Re: Energy Meter (KWH Calculation)

08/11/2009 3:32 PM

sandeepelect,

It sounds as if you have a 3 phase delta generator, in which case only 2 CT's are required to get accurate metering. The current of the phase with no CT must pass through the other 2 CT's, and is fully accounted for. The ending potential of the energy meter will be connected to the non-CT phase.

A gentleman by the name of Blondel established that metering is accurately accomplished with n-1 elements, as long as the VT ending potentials are on the phase with no CT.

You have not specified how you know that the energy is not being metered accurately. If your conclusion was that the inaccuracy was due to a missing CT input, then you are going to find that the metering is appropriate, and the value the meter is showing is accurate within the limits of it's calibration.

__________________
I do not 'know it all', but i will admit that I would like to. CJM
Register to Reply Good Answer (Score 2)
Power-User

Join Date: Mar 2007
Location: Bangalore, India
Posts: 141
Good Answers: 1
#2
In reply to #1

Re: Energy Meter (KWH Calculation)

08/12/2009 12:33 AM

2 CT connection is quite ok. Check the CT directions and connection sequence. Dont what does it mean by it is not matching.

__________________
Best Regards, Shivaram
Register to Reply
Power-User

Join Date: May 2008
Location: San Jose, CA, USA
Posts: 121
Good Answers: 2
#4
In reply to #1

Re: Energy Meter (KWH Calculation)

08/12/2009 12:08 PM

As initially indicated "110V" , the generator has to be Y connected (a neutral point). For delta the only available voltage would be 208V (line-to-line)

__________________
Scientes et audaces fortuna juvat !
Register to Reply
Anonymous Poster
#3

Re: Energy Meter (KWH Calculation)

08/12/2009 8:31 AM

sandeepelect; it sounds like you might have a 3 phase 4 wire system, 200/110 volts 3 phase, 4 wire, then you will need a third CT on the on the wattmeter if it is a 3 element meter it will work. perry

Register to Reply
Guru

Join Date: Jul 2008
Location: SoCal USA
Posts: 556
Good Answers: 23
#5

Re: Energy Meter (KWH Calculation)

08/12/2009 2:13 PM

Just a note for general information; the secondary side of PT's (potential transformers) is usually 110 volts for metering and control circuits. The primary voltage is not indicated by the secondary voltage, however the use of PT's indicates that the voltage is above 600vac.

__________________
I do not 'know it all', but i will admit that I would like to. CJM
Register to Reply Score 1 for Good Answer
Member
India - Member - Electrical Engineering Fields - Power Engineering - Electrical Engineering Fields - Electrical Engineering - Electrical Engineering Fields - Electromechanical Engineering - Electrical Engineering Fields - Energy Engineering - Electrical

Join Date: Sep 2008
Posts: 6
#6
In reply to #5

Re: Energy Meter (KWH Calculation)

08/14/2009 3:33 AM

Dear All,

Thanks for your comments,

But the energy meter was working properly before few days with 3Phase Voltage (110V) and 2 phase CT Input.

Now 1 Phase CT Input is missing. now i want to know That how i can measure exact Generation with the available Energy reading.

Generation Voltage is 11KV.

tHANKS ,

Sandeep Seth

Register to Reply
Guru

Join Date: Jul 2008
Location: SoCal USA
Posts: 556
Good Answers: 23
#7
In reply to #6

Re: Energy Meter (KWH Calculation)

08/14/2009 12:46 PM

sandeepelect,

This new information, that one of the two CT's was not working, sets up a completely different answer. There is not a method of calculating the exact amount of un-metered energy, but there are a few good 'guesstimates' available.

First if there is good historical data, the missing data can be interpolated by comparison with a past period of similar generation.

Second, one of the two meter elements commonly measures approximately 2/3 of the energy, and is known as the 'high registering phase'. The other meter element measures approximately 1/3 of the total energy and is known as the 'low registering phase'.

If a historical comparison identifies the working element, then the math to estimate is simple. Otherwise there is a method based on the vector diagram of the meter elements that will identify the high and low registering phases. Information about the normal running phase angle will be needed to assist in getting more exact estimations.

I would say that identifying if you are 1/3 or 2/3 low on measurement compared to normal is the most complete method of reconstructing the missing energy since it accounts for all the variables of the vector analysis estimate.

Regards, CJM

__________________
I do not 'know it all', but i will admit that I would like to. CJM
Register to Reply
Anonymous Poster
#8

Re: Energy Meter (KWH Calculation)

06/12/2010 3:00 AM

hi,

1.732XVoltageXCurrentXpf

Register to Reply
Register to Reply 8 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); CJMcGill (3); sandeepelect (1); shivaganti (1); tomad (1)

Previous in Forum: Aberrations Introduced by Prisms   Next in Forum: Predicting Mean Bubble Size

Advertisement