Previous in Forum: Common Mode Choke For AC Line filters   Next in Forum: Utilisation of Electrical Energy
Close
Close
Close
7 comments
Rate Comments: Nested
Active Contributor

Join Date: Sep 2006
Location: France (Mulhouse)
Posts: 15

Cable Insulation Voltage Level for Hazardous Area

12/14/2006 9:27 AM

I have a question about the insulation voltage level in hazardous area, exept for Intrinsically safe circuit where the insulation level is clearly defined, what is the minimum insulation voltage for the cable when we have to connecte flameproof equipement.

I know that in France the national rules ask for 1000V (with some minor exeption).

I have not seen clear indication in the ATEX rules

And what about NFPA/CSA?

Thank you in advance for your answer.

__________________
marconet
Register to Reply
Pathfinder Tags: cable insulation hazardous area voltage level
User-tagged by 1 user
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: Cable Insulation Voltage Level for Hazardous Area

12/15/2006 5:52 AM

Go for 1000V, then, if it's available locally. We are talking about armoured cables where the armour is earthed, aren't we? Provided the voltage in the cable is less than the cable's rated insulation voltage the normal cable insulation will be sufficient.

11kV cables can pass through hazardous areas.

For intrinsically safe circuits one can use uninsulated conductors, as the circuit design itself is intrinsically safe. Why one would want to use uninsulated conductors is another question.

Register to Reply
Active Contributor

Join Date: Sep 2006
Location: France (Mulhouse)
Posts: 15
#2

Re: Cable Insulation Voltage Level for Hazardous Area

12/15/2006 1:07 PM

Sorry, i was not clear in my question, i wonder what is the minimum insulation voltage level for the cable.

__________________
marconet
Register to Reply
Power-User
Popular Science - Weaponology - New Member Popular Science - Cosmology - New Member

Join Date: Apr 2006
Posts: 261
#3
In reply to #2

Re: Cable Insulation Voltage Level for Hazardous Area

12/15/2006 3:33 PM

Would it not vary with the voltage applied
to the cable, which you neglect to state???

Register to Reply
Anonymous Poster
#4
In reply to #2

Re: Cable Insulation Voltage Level for Hazardous Area

12/18/2006 4:20 AM

Why does it matter? Will the circuit voltage exceed the insulation rating? If so, then the wrong cable has been selected.

The hazardous area criterion is a "red herring".

Register to Reply
Active Contributor

Join Date: Sep 2006
Location: France (Mulhouse)
Posts: 15
#5
In reply to #4

Re: Cable Insulation Voltage Level for Hazardous Area

12/18/2006 4:31 AM

I try to select a cable for 2 differents applications:

- 24V DC for 4-20ma SIGNALS

- 400VAC for power circuits.

If I Follow the french rules (I am french, but my projects are abroad: middle east, Asia, European countries and i have to follow ATEX or NFPA), I have to select 1000V insulation cable. I would prefer to use lowest insulation level, but I do not know the minimum levels.

__________________
marconet
Register to Reply
Anonymous Poster
#6
In reply to #5

Re: Cable Insulation Voltage Level for Hazardous Area

12/18/2006 5:27 PM

For signal circuits check NFPA. 501.14

For 400V. stick with the 1KV. rating.
Any cost saving you might realise here is not worth the trouble.

Register to Reply
Associate

Join Date: Jul 2008
Location: India, Kuwait
Posts: 31
#7
In reply to #5

Re: Cable Insulation Voltage Level for Hazardous Area

08/03/2010 3:23 AM

For 24V DC use 300/500V rating.

For 400VAC use 1KV rating.

Register to Reply