Tan Delta Testing

08/18/2009 4:59 AM

how can we measure tan delta? why it is neccessary to measure?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Active Contributor

Join Date: Aug 2008
Posts: 19
#2

Re: tan delta testing

08/18/2009 5:34 AM

Hi, Manir

Tan Delta could be measured with a TanDelta Test equipment along with Hi-voltage VLF 0.1HZ source and it should be less than 1.2X10-3 for healthy XLPE cables.

TD is an excellent diagnostic tool for MV XLPE cables.

TD is indication of aging of cable.

As the cable losses increase TD value will increase.

TD is used to optimise over voltage testing and limit the stress of cables.

Good luck

Register to Reply Score 1 for Good Answer
Associate
India - Member - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Feb 2009
Posts: 38
#3
In reply to #2

Re: tan delta testing

08/20/2009 1:47 AM

we are testing in power trafo of 100MVA 220kv/33kv. we apply 2kv and 10kv in trafo for tan delta. result come .004. so what is this .004. is it tan delta=.004 or angle delta=.24 degree

Register to Reply
Register to Reply 3 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); manir_b4u2002 (1); manzoor14 (1)

Previous in Forum: Reactors in Power Factor Corrector   Next in Forum: Transformer Calculation

Advertisement