I am working for electricity distribution company.
In my earlier companies I used to keep only standard inverse curve active for over current and earth fault protection relays in 11kV outgoing feeders. This then very well coordinated with the 11/0.4kV distribution transformer HV side instantaeous protections.
In the present company, since years they have been using instantaneous as well as inverse curves in the outgoing feeders, the instantaneous is set just taking certain times the CT ratio. Many a times during transformer HV side fault this instanataneous element operates interrupting power to other stations as well, when only that transformer protection could have isolated itself. They justify this saying it operated because the fault current was very high!!! I am surprised so what?
Is instantaneous protection required in distribution outgoing feeders? Is it not OK if we clear the fault by inverse element in 300 to 400 milliseconds. Can some one comment on this?